EDF have requested a building be converted to a TT system.
Currently a TNS 2x100a head supplies a shop then a flat respectively.
The are x2 fuse boards supplying the two areas each having 30ma RCD protection on all final circuits.
Am I correct in saying in simple terms X1 earth spike Into...
i done an impedance test between the L-N at the meter and got 0.08 ohms so I don’t even think it’s a broken PME or neutral if that what they meant.
The meter man said to the client with the fuse pulled out he was getting voltage on the neutral.
Unless he has an different means of testing there...
Hello guys
EDF came out to a flat and attempted to replace the meter.
I have been called out to investigate there comments which are “unsafe to remove meter, possible borrowed neutral, voltage at meter even with fuse removed (dropped neutral test)”
First off i am currently on site, I removed...
Hello guys
Client wants to control a load attached to a 13a plug outside.
Initially I was thinking of large ip rated box containing a socket with a WiFi plug adaptor which will be installed outside.
If there an other ways?
installing ip 65 gu10 downlighters within 2.25 meter height of zone one.
What are the hard and fast rules because my reading of section 701 does not permit 230v ip 65 downlighters yet I see it everywhere?
Hello guys
After doing the adiabatic the 6mm will be fine as the main earth on a tn-s 60a 16mm tail fuse board.
Is there any reason past the Calc this may not be ok as running a new earth may be tricky
I am OLEV approved and still not gone through the process.
It looks quite complicated and appears to be risky is OLEV pull the grant money after you have installed the chargers.
What’s the claim process like?
sorry, i was trying to say is there a way i can get away with not using a TT rod for car chargers installed outside on a PME system. (very anxious about banging rods into the ground)
Pod point have a charger however the PME break detection device installed within is not to any BS standard to...
Hello guys
I have a job coming up where i will be installing x2 car chargers in an office car park (wall pods) supplied from a PME.
When installing earth rods what procedures can anyone recommend to ensure you do not go through any services below?
Site drawings would be ideal however they are...
Hello guys
I need to install some external car charges outside in a car park on the wall.
Problem being is that the building has a PME system and there are no drawings of where the services are buried so I want to avoid using an earth steak.
Is there any way I can get away with not having to...