EDF meter change fault | on ElectriciansForums

Discuss EDF meter change fault in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
82
Location
london
Hello guys

EDF came out to a flat and attempted to replace the meter.

I have been called out to investigate there comments which are “unsafe to remove meter, possible borrowed neutral, voltage at meter even with fuse removed (dropped neutral test)”

First off i am currently on site, I removed the fuse and tested potential between N in and N out no voltage.

I then tested all live conductors to earth and no voltage.

Question is what is this dropped neutral test and and I missing something with my testing as I can’t see a problem?
 
I think they have used the wrong phrase when they say borrowed neutral. As above it sounds like a DNO issue rather than a borrowed neutral on the consumer side.
 
i done an impedance test between the L-N at the meter and got 0.08 ohms so I don’t even think it’s a broken PME or neutral if that what they meant.
The meter man said to the client with the fuse pulled out he was getting voltage on the neutral.
Unless he has an different means of testing there is no voltage between N in and N out at the meter or between and earth or live.
Not sure what else I am missing
 
report attached from EDF meter man
 

Attachments

  • [ElectriciansForums.net] EDF meter change fault
    869D4431-D89D-4BB8-8F88-B93A0A4C536C.png
    2.8 MB · Views: 250
Does he mean he gets a voltage on the neutral on the supply side of the fuse carrier or the consumer side?
 
a) So the implication is the neutral (and TNC ) Earth will rise up to Line potential as a load is placed L to N ? ( Depending on additional earthing / Bonding ) Not nice !
Or is it TN-S.
b) Not DNO side
( Or are they witnessing lots of Line leakage into wall , confusing "their volt sticks -perspective on things .. Hope not)
c) Power sneaking into install from leakage - Neigbours outside lights
(More added since Liked..!)
 
Last edited:
It may be a Neutral from another flat (or shop?) within the building.
Are you testing with the C.U OFF, try with all MCB /RCBO ON and C.U mainswitch ON.
Meter person should have had the CU off before pulling the fuse, maybe they didn't.

What about Reverse Polarity at the cutout?
 
Last edited:
What is the voltage between live and neutral? And live and earth and neutral and earth?

L-N 248v
N-E 0V
L-E 248v
[/QUOTE]
Surely if it was a dropped neutral L- n would not be 248 V.

I recon the meter guy has one of those stick voltage indicators and it’s given him an incorrect read, as they do.

Call the engineers and ask him what equipment he used and the resultant reads.
 

Reply to EDF meter change fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top