In my opinion using the Matt-e single phase verison for a hot tub gives you a false sense of security, as it only protects against some PEN conductor faults but not all, it is likely you can have a open PEN conductor and still have a voltage between 207v-253v between L - N depending how the...
Discconect cables at the water and gas pipe end, or maybe they would take a cover off the service head
I don't know for sure, but discconecting the other ends of the cable seems simple to me
How do you figure? for an RCD or MCB achieving ADS in normal circumstances when the PEN conductor is intact then yes Zs etc will determine if it will disconnect in time. But you have no or very high Ze during a PEN conductor fault so any previous measuret on Ze or Zs doesnt help in this...
yeah if underground, making it even harder for separation , doh
On my road i can see the electrodes at the bottom of the poles so bit easier to tell where they are
I see, yes some people mention using an earth mat for a hot tub in this case the ground you would be steeping out onto would also raise in potential so the touch voltage would be reduced
I see what you mean about low risk and practicalities of testing, Was wondering as I have seen some videos...
Indeed,
So if installing an earth rod for an EV charger on a small site with a 1x1m garden so no space to perform a 3 wire test so you perform a loop impedance test on it instead, then how would you be able to ascertain if your to close to PME metalwork
Not quite:
If you were to put a 2m earth rod at the edge of a garden and just the other side of the fence to next door garden there is an underground metal water pipe 1m away from the rod and the pipe was bonded to PME earth
If using a 3 wire test, I cant see how you would detect the presents...
I have done so, have watched the JW videos on it and some others, and I already understood how to test electrodes.
But still unsure how to test if you are in the PME influence area so to speak, if not known you could be a few meters away from a PME bonded water pipe, etc
In which case if there...
Hello
I am wondering what would be the correct method for testing electrode separation distance
For example, if installing an EV charger or hot tub from a PME supply and chosing to TT the EV charger / hot tub, how could you ensure you are a sufficient distance away from any buried PME bonded...
Another thought on the Zappi 2 car charger. It measures utilization voltage and disconnects if outside of the range of 207v-253v and for when a PEN fault occurs where the voltage remains within this range it disconnects if it detects any current flowing on the CPC
Surely this is not automatic...
Just a little thought here,
With PME / TN-C-S supplies being most common, and the difficulty with EV charging from this earthing arrangement are:
722.411.4.1:
(i) = Very difficult to ensure 3 phase loads are always balanced in the real world
(ii) = Unless in a new build with foundation...
Shower = 43.7A
2x Heaters = 26A
Radial circuit on 16A MCB = 16A
Lighting circuit on 6A MCB = 6A
Total of 91.7A or 21.1kw
Seems a lot for a shed, I guess the lighting circuit will be way under 6A & if the 16A circuit is it used for sockets hopefully they won't need to plug any more heaters...
Maybe you could set up a priority unit to turn off circuits when the show is on, etc
Like this:
View: https://www.youtube.com/watch?v=N_jTZbpUfTc
1591785311
Doh, must have posted at the same time !
Are you referring to sockets on a spur off a ring final circuit
As far as i understand it, if it is an unfused spur then only 1 double gang socket is permitted
If using a F.C.U then I think you can have as many as you like as the cable is over load protected by the fuse in the F.C.U.
If more...
I have actually made a light from a trombone. As I couldn't earth the trombone without ruining the aesthetic, I fitted a 12v lamp holder and ran it from a SELV transformer, I was not concerend with the legallity as it is for my own office and not planning on selling them
If using already CE marked and type approved lamp holders, and then fitting these lamp holders into a home made case (almost like making a homemade lampshade)
I wonder is this would comply / be easier as all the electrical components are already exsisting products being put together
I have no...
My personal opinion would be to get a EICR done, which will tell you if the whole installation is safe or not. The fact that is is plastic doesn't mean it needs to be replaced with a metal one provided it meet the regulations at the time it was installed.
It seems strange to me that a ring...
No was not talking about lock out tags,
was mentioning observations in how power is supplied for events, in venues in the US (what we meed to plug into)