  1. TJ Anderson

    Hello, advice and gentle ribbing welcome!

    Are you doing the flat rewires on your own or with someone?
  2. TJ Anderson

    Hello, advice and gentle ribbing welcome!

    2365 L2&3, AM2 and NVQ3
  3. TJ Anderson

    overheard conversation re 3phase working

    Then a large current will flow and the OCPD'S will operate. There are loads of people in commercial and industrial maintenance who don't really know what they are doing too!! :)
  4. TJ Anderson

    Megger 1552 rcd type testing

    Hi Mate Your 1552 will only test Type A and AC. The DC option is for testing DC sensitive RCD'S (not Type B). If you are testing Type B RCD'S you will need to upgrade. The 1730 will test Type B RCD'S.
  5. TJ Anderson

    Installing 4mm cable, installation method

    Hi Sean Yes, you are right. Your experienced sparky mate should know better lol :). The load is undetermined as feeding sockets so it would have to be based on protective device rating. The cable is undersized. In fact, due to the insulation, you should also add rating factors to that which...
  6. TJ Anderson

    Circuit Breaker needed for Split Air-con with Inverter

    Lol. I'm too late again. Yes 12.2A single phase. How far are you running it from supply and how will cable be run?
  7. TJ Anderson

    Circuit Breaker needed for Split Air-con with Inverter

    Assume it is single phase. Not sure what the regs are in Germany. Over here that would get a 30ma 61008 RCD (>16A) in series with a 60898 C16 or instead a 61009 C16 RCBO would be the order of the day. 2.5 or 4mm circuit conductors dependant on PFC at origin, install method, length of circuit...
  8. TJ Anderson

    Circuit Breaker needed for Split Air-con with Inverter

    Just read your last. You need the know the demand of the unit before you can do anything.
  9. TJ Anderson

    Circuit Breaker needed for Split Air-con with Inverter

    You need to know the load of the unit and then size circuit protective devices and cable. Ask the Electrician what supply they require.
  10. TJ Anderson

    BG Dual RCD metal DB's

    Have you tried it with the RCD Load Neutral Terminal disconnected as well as the MCB'S switched off?
  11. TJ Anderson

    IR testing on CU upgrade

    Yes mate, me too, that's doing a thorough job.
  12. TJ Anderson

    Just saw this in the new ‘shower electrocuted’

    Absolute tragedy for that young life. I am really saddened by this as that was so preventable.
  13. TJ Anderson

    IR testing on CU upgrade

    As above. Circuit protection is often altered in these upgrades. (3036 to 60898 OCPD's for example) so to confirm ADS, Zs would have to be taken and recorded as a minimum. Additional protection by RCD may well have been added too and these would also need testing and recording to prove satisfactory.
  14. TJ Anderson

    Replacement Proteus RCD?

    What tests did you do?
  15. TJ Anderson

    Looking for mft 500mA fuses

    SIBA 70 094 63 F500mA 600V x10 500mA Fuses for Megger Testers JPSF003 7009463 | eBay -...
  16. TJ Anderson

    Hello can you help me fix my house?

    Sorry OP you need an electrician with an insulation tester who can use it properly. A good spark will find the offending circuit very quickly and then investigate that circuit to pinpoint issue.
  17. TJ Anderson

    Looking for mft 500mA fuses

    Megger MFT?
  18. TJ Anderson

    Replacement Proteus RCD?

    Save your money on the RCD replacement which won't be required and pay an Electrician to locate the cause of the imbalance. The RCD tripping does not mean it needs replacing lol.
  19. TJ Anderson

    rcd tripping on a ring main

    Absolutely loved that!!! LMAO