  1. Risteard

    EV charger causing ground overheating

    There is no Annex Zb derogation within I.S. EN 61439 so no conditional short-circuit rating for type tested units etc. so there is no prohibition on that. Of course this is assuming that it had been connected correctly e.g. supplied with tri-rated panel flex outer something similar.
  2. Risteard

    MK 5780s replacement

    A charge point should not be sharing an RCD. It needs to be dedicated.
  3. Risteard

    Notifying DNO for first EV install

    I don't doubt for a second that many/most installs aren't notified. Apologies if you thought I was trying to imply otherwise.
  4. Risteard

    Notifying DNO for first EV install

    Yes, but they still need to know how many are in use in the area in order to ensure that the infrastructure is capable. It's not like every installation drawing 60A/phase is no problem for the DNO.
  5. Risteard

    Notifying DNO for first EV install

    Yes it's legally required.
  6. Risteard

    Notifying DNO for first EV install

    You must "Apply to Connect" if the maximum demand is above 60A/phase. If it doesn't exceed 60A/phase then you can use the "Connect & Notify". When I have needed to "Apply to Connect" there has been no real hassle dealing with the DNO here. Can't comment on other DNOs though.
  7. Risteard

    Worst connector ever invented

    As above, in fairness to them all of the Next luminaires I've come across have been good and well designed.
  8. Risteard

    Why do i need a rewire when i've passed inspection with no issues?

    I believe there is a specific job title for people who mate for money ;-)
  9. Risteard

    Why do i need a rewire when i've passed inspection with no issues?

    It's not a Report. It's merely a certificate for replacement of the DB only, so the OP appears to be misunderstanding what it is stating. It relates only to the work carried out and does not declare that the installation is fine.
  10. Risteard

    UK Can you add additional sockets to non RCD protected circuits via RCD spurs or sockets?

    When I've carried out inspections on them in the past I would have to say that that's not my experience of them. I'd well believe the old Bill rewireable fuse boxes being there.
  11. Risteard

    De-rating a ring circuit

    I'd second that. He's a very silly boy (for want of using terms I'd prefer to describe him).
  12. Risteard

    moving an ev charger

    I've never yet come across PAT Testing of an EVSE.
  13. Risteard

    3 phase RCD question

    Anything above 15mA up to 30mA meets the Standard for a nominally 30mA RCD.
  14. Risteard

    Best/ most useful charge points on the market

    There is currently an issue between Easee and the Swedish Electrical Safety Authority, with the potential for a sales ban in Sweden.
  15. Risteard

    Difference between 1p+N and double pole RCD

    Not really relevant with an RCCB. If it were an RCBO then it would lack overcurrent protection in the neutral pole, but an RCCB doesn't provide overcurrent protection anyway.
  16. Risteard

    Best/ most useful charge points on the market

    PEN fault detection and disconnection is incorporated into the Zappi. Same with Project EV (at least if it has PME in the model number). Don't forget manufacturer's declaration of conformity.
  17. Risteard

    Welding equipment - DNO permission?

    Cheers all. Seems that it may not be still a requirement after all (or at least not a widely known one!)
  18. Risteard

    Welding equipment - DNO permission?

    Does anyone know whether it's still the case that if a customer wishes to have a supply installed for a welder in their home that they need specific permission from the DNO? Struggling to find an answer on Google.
  19. Risteard

    Certification software that will work offline?

    The Clik NICEIC Cert Software has an Android app (Clik Cert Electrical).
  20. Risteard

    Circuit numbering confusion?

    Ironically, his insistence on how single phase boards should be numbered, i.e. not based on position of main switch, contradicts his system for TPN in that the single phase won't keep the same position in a bigger board if you number from the other side.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top