  1. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    The C3 was a 70-90mm gap between the existing conduit and the board. Planned to be sorted with boxing in later and grommets. Risk assessment done expected very low risk from the position of the board. Could not physically cause or contribute to an accident short of sticking a fork in it.
  2. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Unless he inspected and tested. Which he could have done. But didn't. (I still find no regulation supporting your view mind.)
  3. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Ah, right. The electrician refused to do the testing based on the C3. Said it failed outright. Periodic inspection and testing every 12 months. I admit it's a weird one. Just my own pondering whether the installer could have given permission to energize.
  4. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Lol no. Just want people's opinions. I'd have tested it, but failing that I think I would have put on one circuit at a time. Until it was all up. There's nothing definite in the regs. Just wondered what the popular consensus was... while I also have a beer.
  5. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    That's what I'm saying though. It's just a board change. There aren't really any tests that are anything to do with the wiring up of the board itself. A visual could confirm that live, neutral and earth cables were in the correct terminals or if there was damage to cables. Tork screwdriver for...
  6. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    As far as I can tell mistakes on both sides. Electrician thought 6-8 hours to install and test. Had to put in extra metal conduit for fire alarm because board had to be moved further left to align the conduit. Board supplied had incomer on wrong side and most CPD's supplied were wrong too. True...
  7. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Ok... maximum security prison. Various high risk prisoners topping themselves and stabbing each other... yes planning should have been way way better... but loss of power was a real H&S risk. Refusing to test it or put it back on for 2 days over a C3 fault? The more I think about it the more I...
  8. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Agree. Conduits line up perfectly. There's about a 9-10mm gap. It's boxed in with no stress or strain & no access. Essentially the conduit is rendered null & void?
  9. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    The reason given for not doing anything was there was a C3 fault. The board installed was smaller than the original so conduit no longer fitted. (Not installers choice) it was planned to be boxed in. This was predicted and reported to management. Knockouts were given grommet strip edging...
  10. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    That was my thinking, system had periodic inspections and the initial verification. Job was planned by the bosses, timing and planning not up to the electrician. Advice to next shift on at 8am to test critical systems given. Client happy to wait a further 4 hours. They neither tested nor...
  11. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    Ok, To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are...
  12. B

    Does a CU swap require a full initial verification on all circuits before it can be energised?

    To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on...
  13. B

    Electricians and Electrical Work During COVID-19 / Coronavirus Pandemic (Public Weekly Thread)

    Offered to work for free a few weeks ago to finish NVQ... no prizes for guessing the outcome.
  14. B

    Electricians and Electrical Work During COVID-19 / Coronavirus Pandemic (Public Weekly Thread)

    LOL been asking around for 3 years. I don't want to sit and watch the tumbleweed rolling by that empty thread either. I'll post you all pictures when it's done.
  15. B

    Electricians and Electrical Work During COVID-19 / Coronavirus Pandemic (Public Weekly Thread)

    I've decided to do my initial verification qualification at tradeskills4u and just do it myself. 16 electrical companies contacted and not one willing to let me help out and get portfolio proof on what is a £1500 3-4 day job. Five of whom I said experience for my son who was made redundant... I...
  16. B

    Recently signed up for a Domestic Electrical Installer course, need help.

    Ah I was watching a documentary about Queen when I signed up. Hence the nod to Mr May. Yeah physical strength is definitely a thing. It depends on the individual really. I do TES for festival stages so carrying scaffolding, trussing, lights, amps and speakers, hoists... box pushing and rigging...
  17. B

    Recently signed up for a Domestic Electrical Installer course, need help.

    Slightly hijacking but I'm female. I have the 3rd year diploma and 15 years in electrical systems design. Couldn't get an apprenticeship 15 years ago. Have to pay to have my work checked over and signed off. Trying again to get the qualifications. No one seems able to cope with me not being a...
  18. B

    Electricians and Electrical Work During COVID-19 / Coronavirus Pandemic (Public Weekly Thread)

    Lost apprenticeship because of coronavirus. Transferring to AM2e as my only hope to get qualified. Need my house rewiring and have money in the bank and public liability insurance... CANNOT find a single electrician near me willing to let me work on it to get my portfolio completed. Rather...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top