I’ve read that, it says that you can have two cooking appliances on the same supply , and on the same switch, I was just wondering whether both appliances would be ran to the cooker switch and terminated there, or should they each terminate at there own individual cooker connection units . It...
Got a new electric cooker and separate induction hob , just need advice regarding installing them , had an electrician in to have a look.
1573771510
Just trying to get some advice, I know cooker has to go on own circuit , but the is a separate hob aswell, hob is 32amps , cooker is 16 amps . I...
Can u run a 6 mm cable for hob 32 amps and 2.5 cable 16 amps off same cooker switch , 45 amp cooker switch wired on own circuit back to cu on 32 amp breaker.
It thought it might be cause some of the loads where still connected, but when testing a rcd , u can normally still carry out the test with loads still connected.