Search results

Search results

  1. S

    Earth leakage

    Earth leakage clampmeter.
  2. S

    Earth leakage

    Yes it is
  3. S

    Earth leakage

    Yes i clamped all lives.RCD has been tested for disconnection time.also the functional test button.
  4. S

    Earth leakage

    Between lines and neutral.its 3 phase.we have measured with earth leakage clamp meter.the best think is,we did with 2 differen clamp meter but we obtained the same results.
  5. S

    Earth leakage

    What do you mean exactly?i am confused. Also the oven is RCD protected and it does not operate.RCD is tested an work well.
  6. S

    Earth leakage

    We have measured 50mA earth leakage from an oven.but during we touch the metal surface we do not receive shock :D how?
  7. S

    2 separated RCD in one grill.

    Its designed to be feeded from 2 deparate supplies
  8. S

    2 separated RCD in one grill.

    Yes it is.but it is not my question.lets forget this unit.just think about what would be happen in this case?
  9. S

    2 separated RCD in one grill.

    I already told you 2 times.the unit is feed from 2 separate supplies.
  10. S

    2 separated RCD in one grill.

    Two 3phase circuit.
  11. S

    2 separated RCD in one grill.

    Yes exactly.but what do you think,use as it now could be dangerous if this scenario shows up?
  12. S

    2 separated RCD in one grill.

    Basically just i would like to know if this situation would shows up,would it be dangerous?
  13. S

    2 separated RCD in one grill.

    Separate circuits.
  14. S

    2 separated RCD in one grill.

    Hi guys!I have a question. We have a 3 phase electric grill with two cooking area and two separated circuit will feed those areas lets say left h side and right h side.Both circuit will be protected by 30mA RCD.My question,is it possible to get a dangerous situation if on both circuit will have...
  15. S

    Unbalanced Delta load

    All right,Thanks man!! :D
  16. S

    Unbalanced Delta load

    Ok,i mean what is happening in the unbalanced delta connection?
  17. S

    Unbalanced Delta load

    Its an oven.the connection is delta.there is no neutral.i have 2 individual thermostat.and the 6 elements are devided to 4 and 2 elements per thermostat.if the first thermostat is on only L1:27 amp,L2:14 amp,L3:14amp. If the second thermostat is on only then L1:0amp,L2:14amp,L3:14amp.If both...
  18. S

    Unbalanced Delta load

    Hi guys. I have an electric oven with 6 elements.the connection, one thermostat has 4 element and the other termostat has 2 elements. Its ,,delta" connected. If the first thermostat is on then: L1 connected to 4 elements. L2 to 2 elements L3 to 2 elements in delta. If the second thermostat is...
  19. S

    Earth current

    Red in this case is neutral.I do not understand your question.So i share a picture.I clamped at both place(like on picture) 1591102191 At first picture is 1 amp.at second more far from earth conductor is around 800 mA
  20. S

    Earth current

    It is internal yes.800 mA around.a bit less but still a lot