Between lines and neutral.its 3 phase.we have measured with earth leakage clamp meter.the best think is,we did with 2 differen clamp meter but we obtained the same results.
Hi guys!I have a question.
We have a 3 phase electric grill with two cooking area and two separated circuit will feed those areas lets say left h side and right h side.Both circuit will be protected by 30mA RCD.My question,is it possible to get a dangerous situation if on both circuit will have...
Its an oven.the connection is delta.there is no neutral.i have 2 individual thermostat.and the 6 elements are devided to 4 and 2 elements per thermostat.if the first thermostat is on only L1:27 amp,L2:14 amp,L3:14amp.
If the second thermostat is on only then L1:0amp,L2:14amp,L3:14amp.If both...
Hi guys.
I have an electric oven with 6 elements.the connection, one thermostat has 4 element and the other termostat has 2 elements.
Its ,,delta" connected.
If the first thermostat is on then:
L1 connected to 4 elements.
L2 to 2 elements
L3 to 2 elements in delta.
If the second thermostat is...
Red in this case is neutral.I do not understand your question.So i share a picture.I clamped at both place(like on picture)
1591102191
At first picture is 1 amp.at second more far from earth conductor is around 800 mA