Thanks for your input.
I know that has been the understanding for granny 13amp leads and why myself have been recommending mode 3 in all previous installs too. But, looking 722.55.101.0.201.1 (iiita bsen 60309 is a recognised socket outlet for that purpose with no mention of temporary use...
Hi to all,
I've been installing hypervolt and zappi units the last couple of years. Recently a client has come to me with Audi supplied 32amp charging lead. It has a 32amp Bsen 60309 commando plug and what looks like a protective device on the lead, a bit like a granny charger.
Assuming i can...
With all due respect, if you're in a position, trained and skilled to be undertaking these works, you should really know this stuff. Especially as part of your scheme membership - these are the basics that you will already have been assessed on...I hope.
Yes, I have dealt with a similar issue before. Client experiencing shocks whilst using their shower. I measured 210 volts between the shower door frame and the MET. Turns out the shower door was fixed through the tiles and into the metal studwork frame of the partition wall. I traced what I...
Thanks for your reply
As feared. Fit anything LED, say a prayer and hope it last beyond 12 months lol!
I might even look at battery and lamp changes on a few units 1st.
Hi folks,
Can anyone recommend a reliable brand for emergency lighting bulkheads please? I have a job coming up to replace 30 odd units.
I have used JCC in the past, to my cost as they had a high failure rate within the 1st couple of years. I've had good experiences with Ansell products but...
Morning all,
I'm wondering if anyone has much experience with the Tesla Gen 3 Wall Chargers? Quick look through the instructions shows no PEN fault detection; easily dealt with using a Matte or similar. Also, I noticed no facility for Load management/curtailment of the installation via CT...
He was ripped off. I felt sorry for him, he thought he was doing the right thing.
More recently, I looked at an EV charger job. Client had an ASAP installed previous year. The contractor replaced the CU whilst there. On a TT system a dual RCD with circuits run off a couple of non RCD protected...
Around 2016'ish one of my clients had an ASHP installed to heat their drafty old farm house. He called me a couple of years after to ask if I could look at his electricity meter. His leccy bill had racked up £5k for an 18 month period. Hate to think what it is now. Combination of thinking he...
Hi
Doncaster EV ultra cable:
Does anyone know what the current capacity of these cables is given particular reference methods?
The spec sheet just says 'Max current' 45amps (for the 4mm) but it doesn't state the reference method.
The manufacturer does have a very handy cable calculator...
I must admit, my set up is not perfect. Been trading for 17 years and always wondered if there was a better way of managing all of the information/time/admin better. I have 2 problems with the idea of management software: 1) I'm tight fisted and don't want to pay for it. 2) I don't think I'd be...
I use a notepad. A list of jobs I've been asked to do. When I complete a job I cross it off. Once every couple of weeks I rewrite the list including new work that has cone in but minus the jobs I've crossed off. I need it simple.