  1. forum2.jpg

    forum2.jpg

  2. forum.jpg

    forum.jpg

  3. banny07

    UK could it be misprint?

    I had a message from a customer to sort out tripping akitchen circuit mcb. I asked him when was installation tested. He sent me a satisfactory EICR page. Under general condition it says high Zs reading. Ze is 7.25ohm. Could it be misprint? what are your thought guys.
  4. banny07

    UK I am getting very high zs readings

    good shout!
  5. banny07

    UK I am getting very high zs readings

    by disconnecing main bonding conductors to water and Gas?
  6. banny07

    UK I am getting very high zs readings

    I will do this when I go back there. I have another mft (1553) which I will be also using . My concern is how to proceed if It also gives same results.
  7. banny07

    UK I am getting very high zs readings

    I didn't know that. I thought zs db/circuit should be tested with all parallel path connected.
  8. banny07

    UK I am getting very high zs readings

    I used 2 lead on high setting when I bypassed RCBO.
  9. banny07

    UK I am getting very high zs readings

    Thanks. point noted.
  10. banny07

    UK I am getting very high zs readings

    R1 and Rn are same on lighting circuit Megger 1741+ . using plug leads for sockets and using original test leads to test lighting circuit. using 2 low or 3 low leads with same result.
  11. banny07

    UK I am getting very high zs readings

    On lighing circuit r1+r2 is 0.86 but zs comes up to 7.66 ohm.on another radial circuit r1+r2 is 0.09 but zs jumps up to 0.52.
  12. banny07

    UK I am getting very high zs readings

    I am teasting ze with main earth disconnected, zdb with earth connected.
  13. banny07

    UK I am getting very high zs readings

    Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
  14. banny07

    UK Two Electricity Meter

    Both CU's are downstairs under the stairs seprated by partiton wall and have seprate doors for cu cupboard.
  15. banny07

    UK Two Electricity Meter

    one house at the moment but customer thinks he might convert it into two flats.
  16. banny07

    UK Two Electricity Meter

    Hi Guys, 4 Bed house I am going to rewire have two electricity meters. Customer want to install seprate consumer unit for upstairs on one meter and downstairs on the other one. Incoming supply is single phase with seprate cut out for each one. my question is wheather it is allowed or not as I...
  17. banny07

    UK type of earthing syestem

    That is very confusing, that why I wanted opinion of other experienced electricians.
  18. banny07

    UK type of earthing syestem

    Thanks. i am confused why the brown tail from neutral is connected to it?
  19. banny07

    UK type of earthing syestem

    what type of earthing syestem ?