I had a message from a customer to sort out tripping akitchen circuit mcb. I asked him when was installation tested. He sent me a satisfactory EICR page. Under general condition it says high Zs reading. Ze is 7.25ohm. Could it be misprint? what are your thought guys.
I will do this when I go back there. I have another mft (1553) which I will be also using . My concern is how to proceed if It also gives same results.
R1 and Rn are same on lighting circuit
Megger 1741+ . using plug leads for sockets and using original test leads to test lighting circuit. using 2 low or 3 low leads with same result.
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
Hi Guys, 4 Bed house I am going to rewire have two electricity meters. Customer want to install seprate consumer unit for upstairs on one meter and downstairs on the other one. Incoming supply is single phase with seprate cut out for each one.
my question is wheather it is allowed or not as I...