Hi
Can anyone confirm. When 25mm tails on a 100amp supply are longer than 4 meters. Do you need to
Downfuse the isolator switch even if cable size is suitable for length of run?
The main tails are sized based on the rating of the main fuse so that regardless of the usage you must use what is standard? I just ask for some different opinions because my boss will probably try to bs his way out of buying some main tails and I need some more ammunition.
Hi every one,
Im new to this forum. FNG!. A simple question that I cant seem to find the answer to is can I run TnE in steel conduit? I know singles would be the best option but the customer has lots of TnE and wants to keep the cost down. I would strip out the cable but I dont have enough...
20 meters of 25mm 4core SWA for sale! anyone intrested? in lancashire for pick up. spare from a job i did but im never going to use it so thought id give it a go on here.
no drum included just coiled up nicely, never been used.
any not stolen haha
samg_4
Thread
25mm
cheap
for sale
meter
meters
never
sale
stolen
swa
thats
What size metal adaptable box is best to drill a 32mm hole to install a 32mm swa gland? and if anyone knows of a metal box with a 32mm knockout, better as i don't have a 32mm drill yet.
yes, there's a insulated CU to bring the tails into, so was going to go through the metal box directly...
A few years ago I installed the small recessed deck kits within my timber decking, due to the amount of lights and with it being external I removed the combined plug/transformer and female connectors pre fitted on each LED cable, I put in my own transformer seperate and connected all deck lights...
Hi this is my first post, so bear with me, if not explaned it good enough.
Just coming back into domestic side of things after 10years on industrail installaion.
Changing cu and tails + earthing, who can we call to get too wire in tails and re-seal meter/main fuse.
I know if I pull fuse...
Greetings.
I have been working with 25mm tails today and had some tight angles to do.
I wonder does anyone have a preferred method for bending tails, sometimes with a tight angle it's not easy to use my hands and I am loath to used pliers on the insulation.
What sort of angle do you think is...
I've recently relocated a new consumer unit, went to the local wholesalers and they did not have 25mm tails in stock. As it's a 60A main fuse (TN-S) I thought 16mm would suffice so happily installed them.
Just checking through the OSG P17 (2.2.3) and it states minimum cable size should be...
Hi Guys,
Have replaced a 2-tier MK board in a restaurant today, but the 25mm tails are set solid in the wall with no hope of renewing to meter elsewhere. They are too short and I have temporally joined them with 60A connectors.
Anyone got any ideas of the best/neatest way to extend...
If a new consumer unit is fitted with 25mm tails from isolator switch to consumer unit should the 16mm tails from the cutout to the isolator be changed also. Note that the isolator switch has just been fitted with new 16mm tails.
Also should the 10mm main earth be changed to 16mm by the supplier?
Hi,
Going to be doing my Elecsa Assessment soon and house i have chosen to do the work on is a TNCS supply 6 way board with excellent access!! :)
currently it has 16mm tails from meter (located about 2M away on ouitside wall) earth is in 16mm and bonding is 10mm so not to bad!
however...
Hi folks. Just like to pick your brains for a minute. The other day I had to fit a 63a 30ma (50a mcb) shower unit for a customer having a new shower fitted who didnt want a new consumer unit (old wylex board). Split the tails with a henley block but what a job connecting them in the unit. They...
hello there
i've been squabbling with my pal about two supplies we have to put in for somebody.
edf are putting in new meters and we have to supply 2x 2 bed flats
i reckon you have to run 2x 25mm swa cables to each flat. (very difficult route)
my mate reckons you can run a 25mm t&e to each one...
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)