would like your opinions lads on using RCD FCUs
i have come across a few jobs recently where no space at CU or rewireble fuses at CU.client wants all
new spots and extracts etc so i have been taking afeed off upstairs cct to a RCD spur(fused to 5amp) and feeding evrything off bathroom from...
17th says that a lightswitch can be 0.6M from the bath/shower edge as long as it is suitable for its position. - Have any of you heard of anyone getting a shock from a light switch with wet hands?? The Switch is existing and obviously best to fit a pull switch ,- but customer knows not to touch...
Can you still install mains voltage extractor fans in bathrooms? I fitted one the other month but a fellow spark just told me they now have to be low voltage?
Hi,
I am looking for sugestions to comply with 17th ed. when making alterations to circuits (eg lighting) in bathrooms. We now have to have these rcd protected. If its a BS3036 fuse box what would be a good way to provide rcd protection for the lighting circuit.
Ive just wired an extractor fan and pump into the lighting circuit of a bathroom and put an RCD Fuse connection unit in line on the whole circuit, lights and all; the consumer unit in the house is one of the old Wylex fuse ones and I thought that was the easier option rather than trying to put...
adasadas
Thread
bathrooms
canada
circuit
circuits
help
help!
protection
rcd
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc