Hi all,
Im still in apprentice stages of becoming a sparky and currently learning allot about 3 phase at college the moment. Can anyone share their knowledge with me on how to correctly calculate the Neutral current on a 3 phase 4 wire star system when there is an imbalance between phases
e.g...
Andy1
Thread
3 phase
attach
calculate
calculation
neutral
phase
roman
wire
evening all
i have come a cross a bit of 6.00 T+E to day feeding a range cooker backed up with a 50A breaker which I will derate as when diversity calculated will be fine.but it accured to me I had forgot how to calculate if the 50A would be OK from the disconection times side of things...
Help with a calculation please?
R2 = (Zs - Ze) x 1000
(L X1.2) - R1
R2 = (3.83-0.4) x 1000
(30 x 1.2 ) - 7.41
= 87.87 mOhms/m
How come i keep coming up with 3401.41??
Next problem
Ze = 0.4 Ohms
Zs = 0.4 ( (7.41 + 18.10) x 30 x 1.2 )
1000
= 1.32 Ohms...
Hi all
I have 2 quick questions regarding domestic ring main socket circuit calculations im hoping i could get help with.
1) regards calculating Itfrom table 4D5 in the regs it states that in order to use 2.5mm conductors that it should have a max value of 27A (ref method C), im unsure how to...
Hi guys , im having a little moment ,
I have a 3 phase supply which is 100 amps per phase.
I need to calculate the max KVA that can be drawn through that.
I think from memory it is 300amps x 415 Volts x PF then divide the total of this by 1000 this should give me the total KVA .
Sorry its such...
iv been asked to install a sub-main to supply a house. The supply is quite far away from the house (40mtr) the cable will be installed direct in ground (SWA)
im abit rusty on my cable calcs and could do with some help and advice. hear is where i am at the moment...
ok so after applying...
Good afternonn,
I am new member in this forum and it's my first participation that I hope will not be the last!
I'm a mechanical ingeenier and I'm looking for the complete and correct manner or formula to determine and calculate a cable section in a three phase circuit.
It will be very helpful...
Hello
Pricing a job that has a 48Kwp system, looking to figure out how to price the A.C. cabling from dist board to Inverter, the run is 80M, any idea?
Your experience aprechiated.
Could somebody please help me check my calculation for amps per phase for a 50KW total load over 3 phases and tell me what it should be.
Thanks in advance.
Hi can anyone tell me the calculation for above? Got the last day of my install of my AM2 tomorrow can't remember from college and havnt had much luck searching, cheers.
When you are detremining the length of a RFC what exactly is its length, is it the total amount of cable you will use or the amount you will use divided by 2?
When calculating the max earth fault loop impedance of a 3 phase MCCB that you use the nominal voltage ie in this case it is on a 60Hz system (120 / 208V ) and a 350A MCCB : therefore 208 / (350 x 10 (C type)) = 0.05 ohms
Therefore Zs is required to be equal or lower than this in order for the...
Just trying to find out what requirements the MCS place on solar PV companies. A few come to mind but are they requirements or recommendations? Would be good to see a full list, does anyone know of one?
1. SAP calculation
2. Structural calculation
3. Correct system design
4 Panel testing...
morning all, im putting a sub main to another db in domestic property currently fed by single insulated 10mm tails. my question is the board will be supplied by a 63 amp breaker and is a 10m run so 10mm t&e was what I was going to use, but after a rough max demand calculation would state I...
hello,
I am using single phase direct driven motor with three speed for Fan Coil Unit. The unit specification shows 350W
I was try to calculate the Power using the equation VI, current reading will get from using the CT meter in particular wire connected to the motor.
Current reading is 0.44A...
Good afternoon chaps....
Just been trying to find a calculator on line, but no joy - Dimplex has one, but not very user friendly!
Have a couple of rooms requiring night stores, so need to calculate the sizes required.
Could anyone please point me in the direction of where I may find a...
Hi All,
I have a site that I believe will be overloading the curent supply and board main switch and would like some input to check my figures.
The client runs a software design company and useage of PC's, monitors & servers is very high. The main intake is rated at 100A BS88 fuse and the supply...