VOLTAGE DROP CALCULATION FORMAT
hi my friends,
is anybody have voltage drop calculation format?
AND THERE BEEN SOME CHANGING OF OPINIONS AND ADVICES AS FOLLOW
1ST REPLY
Shabu there's a few ways of calculating volt drop, the vast majority provide you with an "average" assuming the load is...
ecservices
Thread
cable
calculation
length
reply
sorry
voltage
voltage drop
volts
This is a 2391 question
DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.
45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)...
buttonmoon
Thread
calculation
reference
singles
tables
volt drop
volts
Just need convincing that I am still doing it right!
So,
16mm SWA, 50M run, 12Kw load 3P/N supply. (17.3A per phase)
16mm R1 + R2 = 1.15mOhms/Meter = 100x1.15/1000 = 0.115
ZS = 0.21 + 0.115 = 0.325
230/0.325 = 707A (fault current)
√ 707 x 707 x 0.1
---------------------...
hi
i am doing 2330 and we have been given some calcs to do but the handouts they give are pretty poor
i've had a go at the first one but need someone to tell me if i'm going wrong
( A downstairs lighting circuit of 90 metres is to be wired in 1mm thermoplastic (pvc) twin & cpc
with an over...
How do I work out the following question; When measuring the insulation resistance between live conductors of five existing circuits in the installation the following results were obtained.
185Mohms, 150Mohms, 20Mohms, 200Mohms, 2.5Mohms
State
a)the value of the installation resistance if these...
hi all just going the trevor Linsey advanced installtion work level 3 and i'm struggling with a calculation regarding average induced emf..the Question is :
The Magnetic flux linking turns 2000 turns of electromagnetic relay changes from 0.6 to 0.4 mWb in 50ms. Calculate the average value of...
As above really, just want to double check something.
10.5kW shower, 20m run, under floorboards in insulation, 10mm t&e.
Ib=10500/230 = 45A
As most of the run is in insulation, Ci factor is 0.5, so It must be greater than Ib/0.5
So basically I need a cable with 90A capacity under ref...
Hi
Sorry if I’ve posted this in the wrong area.
Do the tabulated values for the current carrying capacity of conductors in bs7671 include the 1.45 rule of thumb?
I.e. a 32amp type B should trip within an 1hr at 1.45x it’s In (46.4amps)
So do I look for a cable that can take 46.4amps, even if...
Right, this time it is on capacitance... now the equation is simple enough & im sure iv got it right and come to the right awnser in the process however, im pretty sure my tutor said there was a way of making the number that you get back smaller, but i cant remember what he said.
For instance...
Hey. Basically, we are doing alot of calculations in college at the moment on resisors in series and parallel circuits. Iv pretty much got everything down apart from calculating current in the parallel branch of the circuit.
I have a couple of ideas which may be the way to do it, "or not" im...
Hi all with regard to BS 7671 page 48 (411.4.5) can someone tell me in plain English how to do these calculations.
As I am trying to calculate the following question:
The fault current due to an earth fault of neglible impedance in a 400 V three phase, four wire circuit having an earth loop...
Hi,
With reference to BS 7671 on Page 128:
Using the mathmatic formula can anyone tell me how to punch in a calculator the workings out of the following:
When calculating the minimum cross-sectional area of a protective conductor, the following is available:
Fault current = 650A
Op time...
Hello guys looking in,
Just want to make sure i'm doing this right as i'm still a bit fresh,
This is the senerio as follows,
Single lighting circuit from a 230v supply on a 10 Amp MCB.
1.5mm PVC Singles total length from board to furthest point 40 metres.
1500 total watts of various...
kathleenbilly
Thread
cable
calculation
help
looking
question
right
voltage
volts
Hi,
I was looking through old exam papers and came across the following question;
A 2-core distributor cable of uniform csa is loaded as follows:
Point B = 30A
Point C = 90A
Point D = 62A
The cable is supplied at End A at 229V and at End E at 231V. The resistance of the cable is 0.01...
if you were to work out the value of the prospective earth fault by calculation at point of the supply, what values would you need to do this calculation :confused:
Can anyone tell me how to calculate the zs in a 3ph+E installation as my tester will not give me a reading. I've looked into it and a special loop tester is needed, if this is right?
Thanks Paul