Recent thread brought up C3 cables in wall of less than 50mm from surface without rcd or additional mechanical protection on a eicr.
I would also C3 this however how do people feel about this if the walls were metal partions on the studs and not wood?
Would you then be more swayed to a C2 incase...
As it says - what code should I be giving to a metal CU where the cables come straight in through the knockouts without any form of protection. Meter tails and main earth enter through different apertures 'n all.
Hi All
What code would you give for an old Wylex Consumer Unit with a wooden backing, located in the escape route of a communal area?
I was leaning towards a C2 but don't know if I'm being too harsh?
Thanks
hi all, done a eicr recently and found the following and would like thoughts on the codes? Thinking code 2 but bit harsh to fail the installation on these points esp as its been like it for 30 ish years and no problems or atleast that's what the owner will say!!
Cpc used as live on landing 2way...
just done a EICR. good installation, approx. 10 years old. 16th ed.split board, lighting circuits non-RCD, on TT earthing. my query is this:
the Zs readings are high, due to the high Ze, insofar as , e.g. lighting circuits on 6A MCB each have a Zs higher than the max. permissible . should I...
Hello guys
I have an old 1960s flat i have carried out and EICR on, I have come across one issue i am unsure of:
the consumer unit is located within the flat with the meter adjacent, the only point of isolation is the Ryefeild panel outside in the communal cupboard.
Would the defect being no...
My customer read on many forums about people suffering to solve a problem with the above Land Rover with regards to a fault code known as P1260. It seems many people have used trial and error methods to resolve the problem but as far as he could see nobody found a fix, or nobody had posted a...
All trade will get an extra discount. See information here: http://www.electriciansforums.co.uk/electricians-arms/111840-15-uheat-underfloor-heating-discount-code.html - This is strictly for trade only.
You will need to have access to the electricians arms to see that thread. Here's info on how...
Electric Underfloor Heating | Warm Water | Under Floor Insulation | Frost Protection | Uheat sponsor electriciansforums.co.uk and have been kind enough to offer all members of the forum a 5% discount, just enter the code electriciansforum at the checkout for your 5% off.
15% discount is...
3 core Swa feeding ip rated plastic sockets outdoors.
He 3rd core of the Swa has been used as a cpc but the armour is not connected to earth; but has been made off with metal banjos. Would this warrant a C2 or C3? I'm assuming as the armour isn't extraneous a C3? ?
Thoughts please ...
Hello i am a new member and require help! i need a copy of CODE OF PRACTICE for In - Service Inspection and Testing of Electrical Equipment. 4th Edition. Need it tonight has anybody got a copy i can collect tonight cash waiting. I am in Halesowen B62 West Midlands. Name:Jason 07733852222. On a...
I'm doing a EICR on a caravan site. Came across 5 circuits each supplying about 13 16A socket outlets. All are protected by 63 A mcbs and all wired in 6mm twin armoured cable buried underground. The cable rating for the cable is 46A with the ref installed etc.
Im undecided if I should code 3...
Came accross this doing an eicr. How would you code this and the lighting circuits for the house were fed from this. Its obviously at least a c2 if not c1 but ive got to report on it so does it need a separate test results sheet? Its got a 15 amp bs1361 fuse in line and neutral. My thoughts are...
OK.
Doing an EICR on a "chapel" in the middle of a grave yard today.....
So there is a 40A MCB, with 6mm T&E running through the wall to:
Then the 3 x 2.5 mm's each run in surface trunking (the longest run is about 10m) to 1G 13A sockets and at each one there is a wall mounted 3KW fan...
Hi Gents
Just wanted opinions on the above
I know there are various factors that could sway opinion...
Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......
Cheers
Dave
Anyone got any tips for getting hold of spare parts? A customer of mine requires new kids for 4 boxes as part of their tenancy agreement with a landlord. If I can't source the lids I'll have to replace the whole thing and they've been concreted in!! Any help would be massively appreciated, Ebay...
I'm writing up an EICR. On one of the lighting circuits the potential load is theoretically about 1300W on a 5A BS3871 breaker. In reality, the arrangement has been in place for at least 8 years there are no signs of thermal damage, it is difficult to find lamps these days that would max out all...