Hi there i was wondering what code you would give for charred black and melted insulation on line conductor at termination point in fuseboard? the circuit is feeding a wall mounted heater in 2.5mm T and E cable protected by a 3036 15 amp fuse. Is it caused by loose connection what action would...
I'm about to carry out a periodic and after asking other sparks i know (who seem to have different opinions) and reading up from various sources i'm still unsure on the correct coding to put on the certificate.
The PIR is at a shop which also has an upstairs flat. It's a TNS system and there...
DJ Fozzy
Thread
aus
coding
commercial
domestic
electricians' talk
periodic
protection
rcd
hi there i have come across today i ring circuit that twin and earth, however the cpc had been cut out at the fuseboard and at the socket the same. there was earthing from the socket to the metal back box. what code is given here?
1 im guessing???
Hi Guys
I have recently been hauled over the coals for coding items that are not in BS7671
e.g. No lighting in an Intake Room, Asbestos in Switchgear, etc
The customer says its not a reg (I agree) but I coded it a 2 as it needs lighting and is against the EAWR1989
They say I should only...
semaphore
Thread
asbestos
bs7671
coding
electricians' talk
lighting
pir
sheet
I have been given a PIR and asked to do all codes 1 and 2 ok but the tester has applied interesting code2s heres a few the list is not endless.
1 Incorrect screws in panel cover.
2 dust at bottom of d.b
3 No 230V labels.
4 Panel has no markings sayiny 2 different wiring tyopes...
Just to settle few arguments with non electrical based no it alls..!!
No gas/water bonding code 2 :)
absence of rcd code 4 :)
broken socket (faciua intact but switch defective, constantly on) code 1 :confused:
absence of earth sleeving code 4:)
cable sheath on flex not taken into enclosure...
I really need to get this straight in my mind, having not done any PIRs for a long time (since the 16th edition) what is the scenario?
If I am asked to carry out a PIR on a perfectly installed 16th edition installation with no issues prior to July 2008 are all changes that occurred due to the...
nrbspark
Thread
coding
edition
electricians' talk
installation
pir
protection
works
I noticed on an inspection today that all switches I opened to inspect were wired red and black with no red sleeving to identify the black as a live. Seemed to be the same throughout the property although the spark who wired it took the trouble of sleeving at the ceiling roses?!
I appreciate...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc