Working on report at home, left books in office as I got called home urgently yesterday, help on a couple of codings would be useful. I want to have the report emailed off before Monday so I cant use the NICEIC advice line.
Inspected care home, all clients are dementia.
No RCD protection on...
Hi guys,
Just want some advice on codings for an EICR I am doing at communal area in block of flats.all the flats including landlord electric meters and communal consumer unit on wooden board in basement.wooden board is rotten due to dump.which code shall i use?
Hi guys,
Just want some advice on codings for an EICR im doing at a factory.
1-they have wired a radial circuit feeding several sockets in singles using blue singles as a live conductor and black as a neutral.
2-they have 3x ring main mains on 32amp RCBOs type C and all zs values are higher...
Came across this load of s***e when on an EICR today......
The kitchen has been 'rewired' last year for some reason and has been done (very very poorly) in trunking over the front of the tiles. Surface mount boxes have been fitted over the front of the original metal backboxes in the wall...
Hi all,
Just a quick question, just done an eicr in a cafe and office and they have surface mounted modular fluorescent fittings in the cafe area.
Non of the louvres have an earth fly lead connected to them, so just getting opinions from you lot if its worthy of a C3 or am i being too picky?
Matt
I did an EICR on a property today and came across a built in hob with a 45A switch but no dedicated cooker circuit
On further inspection it turns out that the 45A switch is spurred from the kitchen socket ring and feeds a double socket at the back of the built in oven. Both the oven and the...
After going to church this morning I had a EICR to do for a friend where someone had been growing some illegal substances and the police or DNO had removed the meter for evidence. So only dead test can be carried out and it needed a EICR before a new meter is fitted. The RFC is protected by a...
Apologies in advance for yet another Hot Tub TNC-S related thread but I'm just after a few opinions after deliberating for some time on an EICR coding.
EICR at a domestic property was found to have a Hot Tub installed on an outdoor patio which is slate flagstone construction, the hot tub is fed...
So here's the scene
All bonding, impedance values, RCD protection in place.
1) Inside the bathroom outside of the zones a underfloor controller has been installed with no local isolation (wired straight from the board)
I am thinking that its not a code, maybe a note as the only reg i can think...
Hi Guys,
Came across this the other day, a little unsure how to code, I was thinking C3 but would like your thoughts. Obviously been done like this to accomodate different makes of MCB
Evening all..
I have just finished my first EICR! It took a LONG time (10 hours in total - not including writing up the report which I am doing now with a cup of coffee!)
There were many, many faults/problems and I have coded most of them but am stuck with 5 of them and was hoping for some...
Been to carry out a EICR today. consumer a dogs dinner! there are two boards one being an off peak supply. bonding to the gas service comes into the 'normal' unit, water bonding goes into the off peak unit (board now dead) the board is still connected to met.
Im thinking at a push a C2 as...
Interesting job doing a massive eicr on a factory
On a lot of the socket circuits the sockets are wired in singles in metallic trunking with the trunking being used as one of the cpc's it appears.
So two things are the trunking is also being used as cpc for lighting and some other circuits
And...
Fella's
I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that...
Hi all my question is,
What coding is the following.
1. Lighting circuits in property rented to students, circuits chased in walls. No rcd protection.
2. All types of Circuits in a school without rcd protection. Some chased some surface.
Would all above be on a c3 and safe for...
Can anyone give me some advice on coding I recently carried out a EICR on a Commercial premises (communal areas of a block of flats) 3 x DB's all single phase with incoming 3 phase supply with 100A type 2 b fuses with 16mm tails going to each DB - personally I warrant this a code 2 any thoughts...
Hi guys
After advice doing EICR report on a welfare set up on a building site I am after advice on my coding
welfare set up is on a tn-s protected by 100ma main rcd tripping out at 42.3ms at x1 I have some covector heating circuits on a c16 mcb but zs is to high for the c16 what code would...
I need a hand to confirm what coding goes with what please on this house
I have been asked to inspect a house by an agent and this is the situation:
TN-S Earthing (0.4 ohms)
No CPC in lighting circuit with Class 1 fittings
No Bonding to Gas or Water
No Sleaving on any CPCs
All CPCs twisted...