Hi Guys and Girlies,
Looking for advice on using this meter (Megger MFT 1553) for doing EET to find resistance of earth rod on a generator. looking for Ω and Ka.
Hi I have just joined this forum after discovering it through a search engine.
I have a question as regards to testing an earth spike.
I have completed a new installation but would like to test the earth electrode resistance before the supply authority comes to connect the power/metering etc...
Hi Guys,
I use a megger MFT1553 for general testing and will use an EET a few times a year, dont want to invest to much in buying one.
Has anyone come across this or should I leave well alone...
I have a Ze measurement on a TT installation of 134 ohms but the Zs measurement I'm getting on the ring is 25 ohms.
Measured R1 + R2 on the ring is 0.82 ohms.
If Zs = Ze + (R1 + R2) could someone please explain why my readings do not stack up with the formula?
Have I taken a wrong reading or...
Hi All , After looking at installation in an old cottage with TT Supply I have found that i need to install a new earth electrode and wire back to the consumer unit . However physically the only way to get the earth electrode in the ground would mean cabling the earth electrode overhead for a...
whitebeetle
Thread
earth
electricians' talk
electrode
overhead
system
tt system
wire
Using a low ohm meter (or multimeter)Is it possible to place 1 probe on the incomming earth at the CU and the other probe on (disconnected) earth rod to get the resistance of the rod (minus the external earth path which forms part of the Ze, wander leads etc). I know its not the correct...
zion
Thread
aus
earth
electricians' talk
electrode
instrument
meter
method
probe
reading
testing
Hi,
Had to spike a generator down to a Sheet pile today on river side.
Welder cleaned up pile and welded a 12mm bolt to it for me which I connected to, I used ELIT to do test as you would do a Ze reading as I was not sure how to do EET as there was no ground for me to spike to, I got a...
Why would someone want to go and put one in on a PME system?
On a closer examination, I noticed that the main earthing conductor had been removed from the PME cut-out!
So, had the spark who installed this electrode just gone straight in, done a Zs which appeared excessively high without...
Staffie
Thread
and earth
earth
electricians' talk
electrode
tn-c-s
hello there
i'm installing an earth electrode for a three bed house thats never had an earth!!!!
i just wanna know if i definately need a 100ma time delay rcd(100 quid?!)
i've already got a 100a main switch/63a 30ma rcd/63a 30ma rcd split wylex 17th distribution board
is it absoloutly neccesary...
Hi-just a quick one?
I do a lot of testing but i dont often test TT systems.Am i right in saying that the earth electrode reading i get goes in the earting sytem section and not the ze box.does the ze box get n/a entered.i test using method 2 with a multifunction tester[Fluke].is there any regs...
sparky1ste
Thread
earth
electricians' talk
electrode
resistance
system
testing
tt system
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc