Hello, got my Elecsa assessment on 4th january, going to change the cu in my house and use that as assessment job, its simple as only 3 circuits, sockets, lights and shower. But shall i tell building control?? Elecsa said upto me, they dont request it but they will let building control know...
Have been told i shud do a adeabatic for all the circuits i put in
When i have a hi pfc they dont pass allthe time
I take pfc at point served (or calculate from V divided by Zs)
then i times it by itself
then i times it by disconection time (0.1 for type b)
then find the square root of that...
Hello
Does anybody know if 'I' in the equation relates to PSCC or PEFC.
GN3 seems to point to PEFC, but reg 543.1.3 seems to suggest PSCC.
Any ideas?
Thanks
Recent pir i did last week ring main 2.5mm and cpc 1mm so using the equation
If =Uo/Zs=230/0.82=78673.183 so this is my fault current sq root of =15734 x time(type b32 amp)0.1s divided by 115
88.69/115=0.77 so 1mm is cool
looking at app 3 pg 249 in bs7671 cannot seem to see the time...
Could anyone just confirm my results for adiquate earthing size and calculation using the adiabatic equation...
My test was on a ring main circuit wired in 2.5/1.5 pvc..
My supply voltage is 247v
My Impedance is 0.38 ohms.
The circuit is supplied via a RCBO 32a C type
My results suggest that a...
DanBrown
Thread
adiabatic
aus
correct
earth
electricians' talk
equation
size
using
Hi All,
Can anybody help....Trying to establish if I would have to change the mec on a TNS system....
Ok So S=sqr(I2xt)/k
When establishing the value of 't' do I use the characteristics of the distibutors main fuse or the main switch in the CU or I have missed the point entirely?:rolleyes...