Rangemaster classic
Power to main fan oven power light stays on when switched off and element heats up to maximum although the switch works correctly and turns the fan on.
Had a call out at a dental practice at 19:00 last night in the end I left the fault disconnect requiring further investigation.
This fault not the simply resolved call out fault but a "while you're there can you look at" Friday night special.
Very bizarre set up as the building looks to be a...
I will try to explain this as best as I can,
Wired 18 downlights in two rows of 9,
The downlights were wired in 3core and earth cable so two switch wires could be used to switch the downlights however the customer wished. It was opted for the lights to be switched in banks of two on alternating...
Evening all,
Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When...
Brief run down for you all
Checked end to end of ring that’s sound
Meggered LN sound NE sound LE 0.03
Split the ring same stuff
Split it again same stuff again
Long story short stripped all sockets off on the ring and every single leg has a LE fault
Was rewired 2010
Only logical thing I can...
Citroen C4 l 2004 front left ABS wheel speed sensor fault.
Hi, ABS and ESP lights up on the dashboard.
Im getting a reading on Kph when driving on three sensors, except for the front left one.
The left front wheel speed sensor has been replaced plus the ESP module and pump, and the...
I got called out to this today. I was told the main oven fan was working but not the element.
Now normally, we don't get to look at the back, unless it's the fan or thermostat.
But on this cheap piece of Beko $hite for some wonderful reason the element screws in from the back, and this is the...
Hi all,
Hope you all had a nice Christmas!
I'm a college student, (I worked in an office, but I wanted a change so at 30, decided it was time to do something else).
I can't ask my lecturer as it's the holidays, but my brain can't figure this out so hopefully someone on here can help me...
Called out to rental property i carried out an EICR on in March; this year to look at loss of power.
Narrowed it down to the down stairs ring main, done end to ends and ring in tact, insulation resistance failed, dropped every socket and inspected the wiring and socket fronts which 2 i had to...
Strange one today, storage heater was roasting hot at the top but cooler at the bottom. Tested all elements, was getting 23 ohms for each of them so elements are fine, but client complaining that it’s not as warm as it used to be. The charge control clicks on and off when turning, could it be...
Was fitting 2 lights today that had been taken down by someone start of the year so the ceiling could be painted. Cables at light switch were marked L and SW so straight away I was thinking that’s no right. Thought id double check I was getting a neutral at light, was getting 24V between live...
Hi All,
Right, I have a very strange fault occurring so I'll start from the beginning.
I have recently carried out a consumer unit change from an old rewireable to a new split load RCD protected consumer unit. So I had changed the board and put new meter tails in.
I have tested all the...
Hi,
I am looking for an installer to faultfind a Fermax Keypad flat access system Newport South Wales. Someone changed the electric entry lock and since then, the lock has been intermittant, the entry codes only cause a clicking sound from the entry unit (relay working) and some of the buzzers...
Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and RCDs. I have read around this as much as I can but being relatively newly qualified my experience isn't as much as the collective members here so I...
Hi folks
I have a lighting ring that occasionally stops working; when this happens, there is no power at any of the switches or ceiling roses. I've identified the feed wire, and it disappears inside the ceiling in the general direction of the consumer unit. There's no loose connections or...
My C/C on the above van has stopped working whilst displaying "check c/c" & "check speed limiter". Got it plugged in today and come up with -
P0564 C/C MULTIFUNCTION SWITCH CIRCUIT HIGH VOLTAGE/OPEN
P0564 C/C MULTIFUNCTION SWITCH CIRCUIT VOLTAGE OUT OF RANGE
The speed limiter works...
Hello I’m a student learning about industrial wiring and circuits and we’re about to start learning about how to do loop impedance calculations. I have made a drawing of a three phase installation and was wondering if anyone could give me information on how I get the Ze Zs and R1 + R2. How would...
Hello all.
I just signed up to this forum hoping to find subject matter experts. I hope I have come to the right place.
I am part of a project where we are trying to address the below problem statement put out by an Energy company. (Not retailers)
Limited visibility of network status beyond...