  1. S

    High Zs on cct

    Hi all, I have a circuit on a db we have installed which is a long run of cable, the R1+R2 comes out at 1.26 and the Zs is 1.24 , this is on a C20 RCBO, the maximum Ze according to the regs for the MCB side is 1.20 . I know it complies as its RCD protected but how do i put it down on the test...
  2. A

    Slightly high ZS reading

    Hi Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good anyone got any ideas? Cheers
  3. B

    High Zs reading how to rectify

    Hi Guys Just wondering again your thoughts on the following if you have a high Zs reading, what is the best way of rectifying it. say you have a BS60898 mcb type b 32a max Zs is 1.15 ohm. So if you took a reading when measured of say 2.23 ohms what is the best to fix this or remedy it. I...
  4. R

    High Zs readings

    Hi, can anyone help? I've recently carried out a PIR on a school building which has 1 main distribution board supplying 9 other distribution boards around the school. Most of the installation is fine except for a number of circuits which have higher than normal Zs readings according to the...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top