  1. P

    Difference between 250v/500v insulation resistance and 15ma/200ma continuity test?

    Hi I hope everyone is all well. I’ve built a rig at home on some ply to do some testing and fault finding to prepare for my exam and just learn in general… I put 100v then 250v through L & N through a B22 led lamp and also the spur neon to see what reading I would get. They were both the same...
  2. A

    Insulation resistance results weird on actuator circuits

    Interested in people's thoughts/experience here. I've just been testing out the insulation resistance on a 20 year old surface water pollution control facility. It has a large number of penstocks with Auma actuators. Here's the puzzle: on a few of them, the resistance - although passable - is...
  3. KeenPensioner

    Insulation Resistance

    As an adult learner I understand that any equipment connected to a circuit that may be damaged by the IR test voltage should be disconnected. I watched an electrician carry out an EICR on a property I rent. On a ring final circuit he removed the plugs fom the sockets before carrying out the...
  4. A

    Insulation resistance problem

    Hi all, Stuck on another job here IR testing. It's a simple 3 bed semi and after short put L-N at board and testing to earth, I'm getting 0.16 Mohms. I've disconnected main incoming neutral, no surge protection of any kind in the house, I've taken out all lamps and plugged out anything I...
  5. P

    Have I possibly damaged the underfloor heating mat?

    So I’m fitting an electric underfloor heating mat by pro warm. I was testing it for continuity between L N and got 88ohms which is what it should be according to the instructions. It says to do IR test at 500V but it doesn’t say between which colours. So I did L N and got 0.00ohms. Have I...
  6. A

    Help with Low insulation resistance reading

    Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did recently. I joined all 3 phase together to neutral and tested from the busbar to earth. I'm getting a reading of 1.33MOhms, and here in Ireland, we...
  7. A

    Insulation resistance testing live conductors to earth

    Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or a global IR on an entire installation, I usually try to remove all loads, eg lamps, neons etc, but obviously this isn't always possible. So I...
  8. S

    Insulation Resistance Testing Am2 - requires to be tested twice

    Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V DC and then final one at 250V DC when all cables. What I'm confused about is GN3 states: "...sometimes these cables are terminated without further...
  9. M

    AM2S Insulation Resistance Test on RCBO

    Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just one RCBO for the ring circuit. Assuming they want me to do a global IR test, can I take the conductors out of the RCBO, switch it off, and then test...
  10. newfutile

    Insulation resistance problems

    During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral bar it's 116 MegOhms lowest (on the outside bollards). However measuring from disconnected neutrals to earth all read over 200 MegOhms. So it...
  11. D

    Stage 2 insulation resistance test

    I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch, there is no current using equipment connected to the circuit yet as the property is empty. In this situation, would one just make a note on the...
  12. R

    Insulation resistance for devices

    I was checking the IR on a socket circuit and found 0.4M between neutral/earth. The reading came from a garage door motor that was plugged in. once unplugged the IR was good. Does the circuit need to be cleared of all things plugged in when testing or does this constitute as a fault. I was...
  13. Calebp43

    Insulation resistance confusion

    Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old wiring) from one switch to another using 3 core. Let's call this cable 1. After hacking some of the cable out the wall we found that the other flat t and e...
  14. J

    Insulation resistance test

    Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is a new ruling apparently, and without me signing it off as ok, the boat is currently docked, and not allowed to go out fishing. The visual checks...
  15. Pegasus

    Insulation Resistance Test, trying to wrap my head around it

    I am self-teaching fault-finding and testing, but I can't wrap my head around insulation resistance tests. From my understanding you send 500V for domestics down the conductors using an Multi-Function Tester, and the values should be over 1M Ohm, now my question is why should the resistance be...
  16. W

    Insulation resistance query

    Was testing a 3 phase DB for storage heating. While testing I noticed I was getting continuity between 2 of the circuits, which were on separate phases. Each storage heater has its own 20A radial, and when doing an insulation resistance test between 2 of the circuits I get a reading of 0.00...
  17. O

    AM2S Assesment , Insulation Resistance

    Just done my exam, passed everything except Insulation Resistance... I can't think how I could've failed because it isn't the hardest thing on the wrold, Tester was on 500V and I tested circuits separately. Only way I could've failed was how I tested my Ring Final, I wago one leg of ring...
  18. HappyHippyDad

    What are the dangers of poor insulation resistance results between neutral and earth?

    What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the dangers of the above? My thoughts are it may indicate a breakdown of the insulation somewhere. However, what are the dangers of this breakdown between...
  19. S

    For Sale Megger MIT230 insulation tester

    Megger MIT230 insulation tester for sale only reason for sale is because it was replaced with multifunction tester. £150
  20. P

    Insulation resistance of Pink Fibre

    Hi there, Does any one know what kind of insulation resistance to expect for pink fibre wall/ceiling insulation? I'm trying to figure out if the cheap insulation meter I have is actually giving me a reasonable answer. here's a bit of background: I have a GFCI mounted in an electrical panel...