Like that?I hadn't seen Avo Mk8's post when I wrote my last post. We've both written the same thing.
Yes, feed the L2s with the 'live' already present near them, then 6 wires between the two sites. These can be 2 x 3&E or 3 x T&E.
What none of them can be is a repurposed earth wire.
100% the same circuit in the CU. Cant I just use for example 3 core YY cable instead of 3+E? Both boxes are already grounded by feeding cablesThat appears correct. All earth wires must be connected at at least one end to the incoming earth wire, which should be tested to confirm it does actually connect to the supply earth terminal. It is preferable that they're connected at both ends.
It should also be confirmed that both incoming lives are actually part of the same circuit.
No for reasons stated in #16 as one of them will be insulated green and yellow and the cable itself should contain a cpc or earth conductor.Cant I just use for example 3 core YY cable instead
My point is... do I even need to run earth conductors between boxes or 6 wires between L1's and com's would be enough? Will I be actually achieving anything doing that if both boxes are already grounded?No for reasons stated in #16 as one of them will be insulated green and yellow and the cable itself should contain a cpc or earth conductor.
Yes, the cables between the switches should include an earth conductor that is terminated at at least one end but preferably both ends, ie both switch boxes per post#18My point is... do I even need to run earth conductors between boxes or 6 wires between L1's and com's would be enough? Will I be actually achieving anything doing that if both boxes are already grounded?