Hi all on a eicr insulation resistance test between live conductors to earth gn3 says join l & n and test to earth is there any difference between that and testing phase to earth then neutral to earth? As you guys know some boards are a right mess and not in order to locate which belongs to which
Hi all, still training so please forgive my very simple question. Why is it ok to test an appliance at 500vdc when PAT testing but great care should be taken to remove all equipment when IR verifying a new circuit installation?
Is it simply just because connected equipment will make a nonsense...
I am installing a C/U and the kitchen has some old Down lights installed with 10 x 12 volt transformers connected. I know I could disconnect all the transformers but I don't plan to do that as it will be a real pain due to how the plasterboard has been bodged. Some opinions suggest the IR...
Hi I want to test the whole board at once with an insulation test so turn off main isolator and breakers turn tester to 500v? And is the best thing to do, the incoming tails L+N put in a link between them and connect your probes to the link and other to earth also can you still operate light...
Hi guys new to this website just a quick question as it has been a while I have a small 6 way distribution board this only becomes live via a time clock supply wired into it I'm going to be testing this board with a IR dead test on each circuit just to make sure according to guidance note 3 & on...
Hi guys,
I was going to carry out a IR test on a CU with a few RCBOs, but I wasn't quite sure how to proceed. Which neutral do I use - the one on the N-bar or the one going to the RCBO? Because if I use the one from the N bar I will actually test just that short piece of cable and through the...
Hi,
Can some one please help me with this question:
Q: An insulation resistance test on one of the radial socket-outlet indicated zero mega ohm between line and neutral. Explain why the result of the previous R1 + R2 test could not be used to confirm polarity for this circuit.
If any one can...
Hi gang
im currently testing a power station,
ive been told to use method 2 ie link live to neutral and test to earth on all the lighting circuits, which are all in SWA on tray with no switches in the circuits.
all readings ok so far, but the last couple are reading 0.00ohms.
these circuits...
I would like to get a better understanding of what the specific IR test results could indicate. I'm talking more about the below 1MΩ area. I'm talking about.. wet plaster, flooding (sitting in water), degraded insulation etc etc, I realise it wouldn't give the answer but it may help in narrowing...
Hi guys sorry for posting as I know there is a lot of posts similar to this.
my problem Is for my trade test I am a little confused about insulation resistance test. I know most of it for example
lock off at main switch
remove all sensitive equipment
test between live-neutral live-earth...
Hi all wondering if you could help clear something up for me. I was recently working on a three phase motor rated for 480volts a.c and wired in delta. So before powering up I done my dead testing and done my insulation resistance test at 500volts d.c which I thought was correct but read up on it...
hi there I have my FICA in a couple months time and generally feel pretty confident but not too sure about the insulation resistance. I know how to test it just not sure of what precautions to take and how many tests need done? also how many times do I need to flick the light switches so that I...
Hi. Has anyone had a problem with a Megger MFT1552 with regards to insulation resistance testing? All if a sudden mine won't work & displays 500mA. I've tried a couple of new fuses but still nothing. Everything else works fine....
My house, built in 1960, has mineral insulated cabling and a voltage operated earth leakage circuit breaker. We moved in 7 years ago (don't suppose that is relevant though :) )
Due to some rebuilding work the meter needs to be moved, and in preparation for that my electrician has fitted a new...
Hi
I am still training and have a question regarding Insulation resistance test.
My question is when doing the test between live and earth at the consumer unit, what happens to the circuit breakers? On or OFF?
Many thanks.
Hi guys,
Fairly recently qualified sparky here starting to do small solo jobs. I'm interested in views on insulation resistance testing on works to be signed off with a Minor Works Certificate. (Sorry this is a long post but I wanted to cover everything.)
One view on this is that you only test...
insulation resistance test on a EICR/pir
have read in 'unite the union guide to inspect and test'
test carried out with L/N joined to Earth and no need to disconnect loads/vunerable devices
pic1 to test whole insulation, shows link between L/N (incoming) at main switch with supply isolated...
Hi guys,
I would just like to ask if any one could look at my test procedure off the top of my head and give any advice or pointers or whether its too long winded or short. got an exam in 2 weeks so trying to drill it in to this thick skull :)
Many thanks
Safe Isolation has been carried out...
Iam currently on a new build project and I've been carrying out some IR test prior to everything being boarded up. The construction is all timber frames with celotex ply and plaster board, I have connected up the kitchen ring with connector blocks to carry out IR tests and I have been getting...
Can any one explain to me the correct method to test insulation resistance on a 3 phase consumer unit all at once as apposed to testing each final circuit individually?
Especialy circuits vulnerable to test voltage. GN3 states that you connect line and neutral together and test to eath is that...