isolator

  1. A

    Cabling a remote RCD and using it as an isolator switch

    I am drawing up a contract for a job in a domestic property which has a 3-phase Distribution Board and need to supply 3ph to a heat pump that's in the same room. An MCB in the DB will feed an RCD in its own enclosure, mounted next to the heat pump 3 metres away. I know that an RCD is desirable...
  2. P

    Fan isolator

    Hi guys,what code would you give for lack of fan isolator in the bathroom.Thank you in advance for all the answers.
  3. R

    4pole isolator on single phase

    Hi, I have been asked to fit a 32a isolator ready for an air con unit and picked one up from screwfix. Unfortunately the one I have is a 4 pole, can this still be used with 6mm t&e or do I need to replace it with a 2 pole. If it can be used do I just use terminals L1 & T2 Thanks
  4. K

    Boiler Isolator

    Hi All, I've just had a new condition report. He's given C2 for no fan isolator which I don't agree with. He also given C2 for the boiler being on a plug/socket rather than a DP switch. I really can't see that being potentially dangerous, what do you guys think? Also the free standing electric...
  5. R

    Isolator for AHU

    Hello guys I've been having quite a nice run where I haven't come up against anything that I wasn't already familiar with until today that is. Hopefully someone is about as I've kind of already ploughed in. Obviously I've made sure it is safely isolated. I though I better just have a quick...
  6. P

    Main isolator replaced with RCD

    A POST FOR DISCUSSION An EICR in my rented flat concluded that an RCD was required among a few other small jobs. I was away while the remedials were carried out but these photo are of the work which was done. The double pole main isolator was removed and replaced with the 80A RCD and among...
  7. J

    Do I need a TP&N fused isolator?

    So the situation is this: Historic 4 story townhouse to 4 flats conversion. Supplier 3-phase cut out coming in at basement level (One of these will have a 60amp fuse, unsure whether the other 2 contain solid links or additional 60amp fuses yet). 1 phase feeding basement. 4-core SWA containing...
  8. C

    UK New timed fan isolator and switch... but lighting circuit is via

    Simple replacement of an old noisy fan. Should have been rip the old one out, put the new one in. Only change is the new fan has a timer overrun which was chosen due to the old tenants leaving it in for so long it eventually went bust. The old fan didn't have a timer. Anyway... I've got the new...
  9. happysteve

    They want to install a smart meter... but won't fit an isolator... which my old meter has built-in...

    An interesting phone conversation with my own electricity supplier (Good Energy) which was very disappointing, and made me sigh (professionally) :( They phoned out of the blue to ask if they could book a date to replace my gas and electricity meters with smart versions. I said I'd probably be...
  10. A

    Multiple fans off one isolator

    Hi folks, Homeowner here. I'm in the planning stage of a project, seeking advice from professionals. I need to upgrade the ventilation in my home following advice from a surveyor. The plan is to replace my one bathroom fan with two fans (one shower extractor and one MVHR unit). In addition, I...
  11. J

    Horstmann electronic 7. Cant get hot water regardless of what I do

    I have moved in 3 days to a flat which seems to have a lot of problems. I have not had hot water yet and the agent tells me I will pay for a call-out if it will be something simple and I could have found it on the internet.. So I am paranoid. The red light is on. I usually would have a shower...
  12. C

    UK Hi Guys, is there a requirement for the metre isolator switch to have metal enclosure?

    Hi Guys, is there a requirement for the metre isolator switch to have metal enclosure?
  13. C

    EICR C2 for lack of isolator switch

    Hello - my sister has had an EICR done for a small flat. There is a C2 for "ensuite no fan isolator" and a C2 for "no isolator for immersion". Just asking if an isolator is a definite requirement for either of these? The immersion is on a radial with its own circuit breaker.
  14. S

    2.5mm2 cable with 32A isolator

    Hi guys, I am going to install a device, it is running microwave magnetron up to 2kW, with power supply of 230V/Single phase/ 50Hz. According to manufacturer's instruction, it supposed to be connected to a 16A MCB/isolator for protection. The problem now is that the location only has a 32A...
  15. Spike1947

    40A Isolator MetalClad or ABS

    Hi I am wanting to purchase a Metal Clad or ABS 40A RCD/MCB isolator to feed a 40 Tube Sun bed, not quite sure whether to get just the 40A RCB or get a 63A RCB with a 40A MCB , something on the lines as per pics shown, I need it to be as small a foot print has possible. cheers Spike
  16. P

    Does this main isolator switch require a separate enclosure ?

    Hi Everyone, Thank you in advance for your assistance, I"m assuming that having an unenclosed main switch is against the rules ? Should it be sited within the same Consumer Unit or a separate enclosure ? The Consumer Unit, meter and main switch are housed within a wooden formica cupboard (2nd...
  17. D

    BS No for Bill Fused Isolator

    3ph 60 3036 fuses, looking for BS No for the EICR?
  18. D

    EV charger SWA isolator switch

    I am considering fitting a car charger using 6mm SWA to a new isolator switch in the meter cupboard and then 6mm T&E to the CU. It would save running the SWA all the way to the CU. Does anyone else do this and if so, which isolator is best for SWA? Thanks
  19. D

    Is a fused double pole isolator classed as a consumer unit.

    I’ve just replaced a faulty 63A double pole isolator supplying a feed to a consumer unit several meters away to a flat. ive come to do the notification on the niceic web page and there is no appropriate category to tick other than circuit addition or alteration in a special locatiom install a...
  20. G

    Location of bathroom fan isolator switch

    Hi all, I have been asked to fit an extractor fan to a bungalow, normally I chase out a box for the fan isolator and locate it above the bathroom door, is there a reason I cant locate it in the loft, im guessing due to accessibility or something, but just wanted to check? Many thanks, Martin
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

TrueNAS JBOD Storage Server

Back
Top