Hi all
Just checking this procedure is correct for Ze
This is a live test so with the consumer unti front off i would lock off main switch keep RCDs on and all MCBs on.
Dissconnect the main earth.
Now on the megger 1553 i would set it to no trip and use the 3 lead method ?
So green...
Hi all R1 + R2 +Ze this equates to Zs but does this also equal the earth loop impedance, can I calculate ELI instead of measuring it, or are there other factors involved?
The value of Ze on a TNS system useing an earth loop impedance test Instrument
list the steps in the procedure and the reasons for each step, I think this is right ?
1.Select appropriate test Instrument - It needs to be able to read Ze (low ohms resitance metere ?)
2. Perform safety check (...
Hi. This seems like a newbie question but please help.
Received the test results with an 'excessive earth loop impedance' on one final circuit. Circuit originates with a 32A MCB and serves 10 socket points. Wiring is 2x2.5mm live, 2x2.5mm cpc. Max Zs = 0.72 Ohm. r1 (line) = 1.68, rn (neutral) =...
I'm going to be fitting a new CCU where the earthing arrangements at the property are TT. Obviously I will need to measure the electrode resistance to earth and as I don't have an earth resistance tester I was hoping to do it as described below.
I assume the result is the number I enter on the...
Hi,
I have a my am2 practical testing exam next week and I'm confused about the earth loop impedance test.
The centre use a three lead instrument, I just want to know if this is right.
Connect the third lead to the neutral bar, and connect one lead to the earth bar
Then measure over the...
Can somebody help me on how to test the earth fault loop impedance(Zs) of the following circuit Cooker,Immersion,motor .i have tried but the tester display :confused:
I was doing a Ze test today with my 1651 fluke and it was reading >2000 ohms.
The main switch was isolated and the earth disconnected. I had the green probe crocked onto the TN-S clamp on the incoming main, the blue on the neutral bar and the red on the supply side of the main switch...
Hi I must admit it has been years since I did this test
State two conditions which were confirmed by the test instrumement before the Loop Impedance Test can proceed?
hi
i am doing 2330 and we have been given some calcs to do but the handouts they give are pretty poor
i've had a go at the first one but need someone to tell me if i'm going wrong
( A downstairs lighting circuit of 90 metres is to be wired in 1mm thermoplastic (pvc) twin & cpc
with an over...
Hi All,
Q: If an earth fault loop impedance instrument records a valve of 0.55Ω at 20°c, what is the corrected valve ( Using the rule of thumb method ) to allow for conductor maximum operating temperature?
Any replies will be appreciated.
Hi All , I am new to this forum but am an industrial electrician (20 years) but have been using my Robin KTS1620 Multi tester in my house to do a few tests as i am considering returning to partp work as my industrial work is quiet.
The house is supplied by a TT System through a 100mA RCD.
I...
The Big Red book states 1.44 ohms for a 60898 / 61009 32a B rated breaker / RCBO The GN3 staes 1.16, I know this is allowing for temp rise on the faulty circuit but what do I put down on the Domestic installation cert, 1.44 or 1.16, according to Harry Hill there's only one to find out...
Hi all,
This is my first post on this forum, so please be easy on me.;)
We currently have new Merlin Gerin consumer units installed within Aberdeen College, and looking at table 41.3 b the eli readings should be 0.72 minus rule of thumb. This fails most of the existing circuits. When i...
Dear All
A mate of mine recently asked me to look at his installation. It has been wired to the 17th edition and all looks kosher, but when I carried out some testing I discovered that it had High impedance values. I disconnected the Main earth that had been connected to an earth clamp, attached...
Hello everyone
I was wondering if it was possible in a TNCS system to add an RCD to a final circuit with a loop impedance exceeding the values stated in tables 41.2 - 41.3 to ensure fast enough disconnection during an earth fault. I had thought it was but if so why are RCBOs subject to the same...
Table 41.3 gives the maximum earth loop impedance on a type B 32a breaker to 60898 as 1.44 ohms, the testing schedule on the domestic cert asks maximum permissble loop impedance, in the test and inspect notes I seem to remember that you are required to write the full 1.44 but I'm sure that you...
Hi everyone
Would be really grateful for your help on this.
I have my 1st NICEIC assessment on Monday (am bricking it) - anyhow I only have an old table & I need one like you get on the back of the proper NICEIC pads - the most up to date table.
Has anyone got one they could send me so...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc