max | Page 10

max

  1. H

    Max Demand

    Hi all just got quick question 60 A Main service fuse total house rewire worked out tat Max demand using x 0.4 will be 64.8 A just wondering if it might be worth giving DNO a ring to see if its possible to upgrade to 80 A main fuse is it worth ringing?
  2. Mark.W

    Max output current of inverter

    Hi guys Can someone pls tell me if the max output current (iacmax) on an inverter data sheet is the max output current per inverter or per phase! Thanks Mark
  3. C

    Max Zs exceeded from generator

    Hypothetical situation, power supplied from a generator - So a temporary installation. BS 61009 Type C 100mA RCBO – 32A fitted at generator Cable run is approx. 300m, in 4mm HO7 Rubber PVC flexible cable ran outdoors, terminated in a 32A socket (single phase) Ze = 0.03 ohm Maximum Zs is 0.72...
  4. S

    Max demand on a unit

    Guys, I have been asked to calculate the maximum demand for a DNO who want the information before upgrading the metering to 3 phase. The client has 3 phase coming in to the building but only single phase meter. The building is a small commercial warehouse unit (4m x 6M) with some upstairs and...
  5. R

    Max allowed on 60amp incomer

    My cleint has a small holiday lodge and wanting to remove hot water cylinder and night storage heaters and replace with instanious water heater and panel heaters. As he is only in lodge a day here and there. The plan is to replace old fuse box with new 17th ed consumer unit. Which will include a...
  6. F

    Max wind speed on roof?

    Hey guys can anyone clarify for me the safe working wind speeds for working on roof? All i can find is 17mph but this is for roofers and scaffolders and not specific to PV. Anyone? Thanks in advance :tt1: Fiardor
  7. L

    Tail sizes - max demand suggests too small

    Fellas Im just writing up the 5 flats I inspected last week, all the service heads/fuses are new to within 3 years, the cut out fuses are all 100A and tails all 16mm, I know discretion is sometimes needed in this area, on some flats the Max demand reaches 90-100A whilst in others 65-75A, would...
  8. R

    Max conductor size

    Hey all, anyone know the max conductor size for an mcb?
  9. A

    Typical Max. demand for a medium commercial premises?

    I'm doing my 2396 design project, and would like some clues about typical commercial installations, and their maximum demand and incomers. Its a large Argos style shop, I've got the max. demand at 500Amps, that could probably come down to around 400 or so with diversity, that'd give me a TP-N...
  10. Toby Kuhnert

    MAX Ze value for TT?

    Hi, I'm in my second year at college, but I'm a bit unclear on what the max Ze should be for a TT system. I know that the regs say 200ohms, and my tutor said that it would be acceptable if you found an earth rod which gave a reading of 200ohms. However several of my mates who have been qualified...
  11. F

    TT Max zs

    Hi People, Just had a friend call me asking what the max zs is for a 3 phase, c type, 60898, 40A when its on a TT supply. The supply to the board is from an rcd 300ma, he says the niceic front page in installation book says 0.46 ohms but he's getting results of 4.03 ohms. I told him as its a...
  12. marksparky

    max zs on a tt system

    hi folks was wonderin if u have a tt system with a ze of say 113ohms, and a circuit say lights with a r1+r2 of 1.33ohms, in the section on test results were it asks max zs allowed by bs7671.... the answer for a type b 6amp mcb would be 6.13. So if my zs is ze..113+ (r1+r2)1.33 =114.33 which is...
  13. I

    existing electric shower re max demand

    hi i have a 60 amp main fuse supplying 63a main switch in cu. my question is about OSG table 1b max demand figures (calculations). When applying these figures ie no diversity for shower, no diversity for first ring main it seems that any installation with a 60a main fuse cannot have a electric...
  14. A

    I was looking for some Info on Max Zs for Merlin 947-2 MCCB`s and found this

    Filling in a EICR i needed values for max Zs I looked for ages using Giggle and eventually found this link http://pws.schneider-electric.co.uk/internet/pws/literature.nsf/luAllByID/NKIY-5JUHSL/$file/MGD5032_section2.PDF/ hope it may help some folk. I may even find it again when I need it...
  15. L

    LED GU10 lighting max number per circuit , circuit design, dimmers

    Hello everyone, lately alot of customers have been asking to change there standard 50watt lv halogen spotlights for the more energy efficient LED gu10's. My question is... is there a max number of these that can be on a circuit? Previously the rule of thumb was 10 but with the loads...
  16. Amp David

    Volt Drop calcs max load help.

    Looking at a job at the minute which is only for 3 IP rated double sockets down a garden. Problem is the garden is almost 35 meters long, then its another 21 meters from switch fuse in the house. Anyway, what I need to double check is when choosing cable sizes for my runs, what is best to...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top