Hello,
What would be the max Wattage immersion heater I could comfortably install on a dedicated 60A circuit?
Not DIY but trying to figure out some options before speaking with contractors.
Cheers!
An electrician once told me that I should always be careful not to exceed too much wattage on each circuit in a house by replacing light bulbs with brighter ones that are of higher wattage (e.g. don't replace all 60W bulbs with 75W or 100W bulbs).
However, with the newer CFL and LED replacement...
If the max Ze for Tncs is 0.35 but you had a 1361 60amp fused isolator before the c.u with the 1361 having a max Zs of 0.56 (from the 80% chart) if the recorded reading at the c.u was let’s say 0.47 ohms would that now be considered to comply? i can’t see why it wouldn’t.
Hi
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a small metal container housing TPN pump control gear to control two TP 24KW .8 PF pumps (to be fair one is a 15kw, but allowance to swap out one for a...
Distance from D/G socket to extended pull out kitchen tap ? Kitchen tap when pulled out is easily with 400 mm of a D/G socket . Not my job . Just asking for clarification etc
Had a bit of a brain freeze. Got to go and do an inspection on a property with 2 consumer units, the 2nd fed from the first on a 50A MCB.
Let's say theoretically I get 0.2 for the Ze on the main board, then 0.3 for the Zdb at the second board and 0.2 for R1+R2 on a ring final on a 32A MCB.
Is...
I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on an oven rather than a 32 amp. Is he right?
This isn't sitting right with me.
So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with
1 RFC 30A (no diversity)
1 Cooker 30A (no data to hand, plate has socket, assuming 21.6A for now)
1 Shower 30A (7.5Kw - full rating)
2 Lighting 5A ( 21 points total * 100w * 0.6...
I know main bonding to water and gas need to be 0.05 ohms
But what about the main earthing conductor?
Does it have a maximum resistance value from MET to the CU?
Hi all, I have brought a fluke 43b to log a local farm to see how many amps they are using at maximum demand.
The meter gives 3 readings for each time interval. Min, max and average. I would understand if the readings were between 2 time periods, but don’t understand how you can have three...
I have set up a sub main supply to my shed as follows:
32A MCB on main fuse board
6mm T&E
Sub-mains board (B&G with RCD (40A 30mA))
32A MCB
4mm T&E @ 3m
Terminating at X2 double sockets
I have been told the sockets could melt as they will only be rated for 13A plugs, not a 32A radial in 4mm...
Doing a complete rewire on a domestic property. The client is adamant that he wants the consumer unit flush to the ceiling not complying with the 1350-1450mm requirement. I have shown him Approved Document M but he’s having none of it.
What would you do in this situation?
Hi,
I have a product in which 5v 2.5 amp adapter (input 230vac 0.2 amp max) used. The adapter is burning out sometimes usually when I connect it to the one of the phase (in 3 phase line where ac >30 hp motor is connected) carrying upto 50 amp current.
Now my question is why the adapters are...
Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and...
I can't find anything related to this in the regs so I probably misunderstood the question. The way I see it the max Zs for any lighting circuit depends on the circuit breaker for that circuit.
Say we have a lighting circuit with 100x36W ceiling lights which gives us a load of 16A, we choose the...