Testing during a board change, a RFC on a 32A 60898, with rcd protection, you find that the max Zs is exceeded by 0.1 ohms using the no trip setting on your mf tester
On the EIC do you -
A) simply record the actual measured value
B) record the actual measured value and note the position under...
Testing a school which has had lots of LED upgrades with exor controls. 12 way unit above the suspend ceiling with flex's down to the switches. All the leads were 12/14 meters long with the most of it thrown across the ceilings like spiders wed. I use to have a table of max loads and sizes but...
Hello,
Having a bit of difficulty completing the below assignment, wondered if anyone can expand on this?
Explain in detail the relationship between the Protective Device and the Earth Fault Loop Impedance, Maximum Zs for the protective device and how this is calculated, Maximum disconnection...
Im specking a large 480a cable over 160m ive done cable calcs and come up with 2x 120mm 70c armored.
now Im trying to work out my max zs...with no avail.
my main ze is 0.17 but my mccb is saying max zs of 0.054 and my mccb will not trip... why is it so low?
its impossible to get my zs less than...
Hi, is there a max distance an fcu can be from an appliance ? Im looking to fit a wall heater on a dedicated circuit; I know the fcu needs to be near to the heater for isolation and maintenance ? I cannot find anything to define "near", in Reg 537.3.2 at least. Anyone know ?
Hi
Just wondering if someone could help me out with this one
Basically I'd like to know what's the maximum load (single phase) a 4 core 6mm SWA could deliver if cores were connected in parallel
SWA in buried under ground and the length is three hundred meters
The cable used to supply a 3...
Hi all, could anyone please explain the necessity for multiplying cpd max Zs values (tables 41.2 ect of the byb) by the rule of thumb value of 0.8 ?
Is it to allow for discrepancies in tripping times (for example a C type breaker trips between 5 - 10 times its rated current) ?
Im assuming that...
Hello all,
i posted this in the electrical theory section but with no responses I thought I would post here as well - since originally posting I have spoken to ELECSA and they have basically said I can use any basis I want to calculate diversity so long as I document what I used and why which...
Has anyone any views on max Zs for say a type c 32a rcbo at 80% is 0.54 and 100% 0.68. I am currently testing a collage and all ring circuits are type c and I am exceeding 0.54 and 0.68 this is a TNCS system so to my knowledge table 41.5 in regs which tells us 1667 for 32a rcbo for TT systems...
could someone please help me quick its fairly easy,
left my regs book at work and cant seem to find the tables online, recieved a snag sheet from a test saying a tp breaker needs down rating from 100a to 80a
they are 25mm type of wiring b, ref method b
i thought of the top of my head they...
Hi I am just doing a renovation / upgrade on a small house and as kitchen plus all downstairs was on same ring final I have broken it up into a separate kitchen ring and downstairs ring and renewed best part of the cabling as it was really old stranded earth steel looking junk cable and not...
Hi everyone, does anyone know or know where I can find max Zs value for 750A BS88 gG fuses. I did a periodic during a shutdown last week an was rushed of my feet. I can`t find anything on the web and can`t get back in to check the manufacturer.
Morning
i have calculated my max demand as 69.6a (sum of mcb's x 0.4)
and on my eic i have n/v the main head fuse- but on the sticker it says 60/80a (i know it could actually be 60 or 80 or 100 inside)
this is the job i am using for my niceic initial assessment
will this be asked about by...
The heading of table 41.3 says it shows " max earth fault loop impedance Zs for Circuits Breakers..... giving compliance with 0.4s disconnnect time of 411.3.2.2 and 5s disconnnect time of 411.3.2.3."
411.3.2.2 is for final circuits not exceeding 32A. 411.3.2.3 is for distribution circuits and...
Just going over all these changes brought about by amendment 3 and familiarising myself
with the new max Zs and I understand how they are arrived at using Cmin to reduce total by 5%
and the question is on a 30ma Rcd is the max Zs still 1667or should Cmin be applied and reduced by 5% ?
if not...
So, when I did my 2391 I&t course I was told to use to values in table 41.3 of the regs for max ZS value for rcbo which provide earth fault, and over load protection. Recently a colleague of mine said you should use the value in table 41.5 which states a max permissible ZS of 1667 ohms. I don't...
Can someone help confirm what the max Zs for a 50A BS3871 type 4 Mcb?
Am I correct to use the equation 230 / (50xIn)?
Using that equation it comes to 0.092.
Theres not much help in the regs!
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc