Hi.
Question regarding maximum demand calculation.
I have a customer which wants to have a second kitchen fitted in the house. Is this at all possible?
There are two consumer units in the house.
One which has following circuits:
oven 40A
hob 32A
ring basement 32A
ring gtound floor 32A
ring 1st...
Hi guys, I am after bit of advice regarding calculating the anticipated maximum demand.
I dont know a lot of details about the install apart from: It is a 3 phase pme, 100A cut out. Light industrial use. I am calculating small power and lighting only, no mechanical. Lighting will be LED. The...
Maximum ID for 2mm2 wire crimp
Does anyone know what the maximum Id would be. We are using CE5 connectors, but different suppliers suggest completely different wire sizes as suitable.
Hi.
I have have tested a property with a TN-s system and the main ze reading is 2.98 ohms which is far to high for a TN-s system which needs to be within 0.8. What would be should be done in this situation? Contact electric board?
Thanks.
Hi I have a Fluke 1653b and it claims to have Pass/Fail indication on RCD's ?? Where? Is this on the auto mode?
I can only get it to auto test then I have to scroll through all the measurements. There is no mention of this feature in any of the manuals?? Help!!!
Thanks
looking to get a bit of help got a job that currently has 8 flats and a landlord supply and a big office on the ground and basement
After using the OSG for diversity have come up with the following
118A per flat (no gas)
127A for landlord (lift etc)
180A for office (air con)...
Hi guys
Basicly iv got a 6 bedroom house
100A bs 1361 single phase supply
main fuse board is new with 25mm tails with 2 spare ways
would a extra submain fed by 25mm tails for the origin support 5 shower circuits say 40A MCBs 10mm cables 8KW showers
taking into consideration diversity would this...
Hi guys, I'm looking to install a sub board to feed 4x 8.5kw shower circuits and 2x 2 ring 3kw hob circuits (4x32amp MCB's and 2x16amp MCB's). What would be the best method to work out the maximum demand? I get 83amps. Many thanks in advance.
I'm intending to finally refit my bathroom, first thing I want to get sorted before I start removing tiles and making a mess is the maximum KW shower I can currently install and what are my options as my current shower suggests my electrics may not be suitable for modern showers.
6mm cable
The...
Hi Everyone,
I'm trying to determine, for the network shown below the value of the load Impedance that will dissipate the maximum power and the value of this power.I already calculated the Rth , but I'm stuck on P=I2R.Can someone help please?
Thank you.
Good afternoon all, firstly im pretty rubbish at cable calcs. My question is this, the load on the circuit is 6.6kw for a outdoor ev charger so the cable would be clipped direct. Using 4mm NYY cable is ok subject to the cable length, any ideas on the maximum cable length before having to use...
Hi all, Scenario: A fused spur unit added to a ring main to supply several window actuators via an open / close rocker switch. The ring main is protected by a 32 Amp type B Mcb, the fused spur would only require a 5 amp BS 1362 fuse (lets say a 13 amp for worst case scenario in case replaced...
Hi, what's the maximum load I can run from a shaver socket in a bathroom? Can I run speakers in the bathroom from this point?
If that load is maximum, can I put extension cable into the bathroom and how long does it need to be away from the shower?
In preparation of wiring up a commercial premises (function rooms / bars / restaurant area) I am trying to determine to what extent the existing 60A single phase supply might need upgrading. I have not had to do this myself for a commercial premises, and I am wondering if the same rules apply as...
Currently completing 2396 project (cant wait to see the back of it!!) Would just like to check im on the right wavelength when calculating max demand and diversity
DB1 Maximum Demand & Diversity
Lighting - 90% of total demand.
Total demand of lighting circuits is 50.48amps. After...
In my latest exam a question asked:
what is the maximum test current for a 100mA RCD,
50mA,
100mA,
150mA or
200mA
I think I have revised so much by brain has turned to mush! I believe the answer is 100mA but could someone please confirm?
Hi guys I'm after a bit of help with working out my Max Demand normally in a domestic situation its fine but theres so many heaters and water heaters on this that I'm a bit confused.
I have been asked to do a bit of commercial installation for a kitchen and toilets its a children's soft play...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc