Hi all
Wondering if you can help...
I'm in the process of buying a flat and I had an eletrical report done. It says there are some things that need to be done as outlined below. My dad is good at DIY and we're thinking about doing this work by ourselves - or at least some of it. Ideally if I...
carve
Thread
electrical work
electricians' talk
following
inspection
periodic
work
Hi just trying to clear a question up,reg134.2.2 states the designer makes the recommendation for the first PIR to be done.
GN3 page 19 2.5 says the inspector is the person to recommend the first PIR,
which one is correct?
parker56
Thread
electricians' talk
first
inspection
inspector
periodic
Hi everyone,
Hope you are all enjoying the last Bank Holiday befor the Christmas rush starts !!!
Anyway, just a quick question to clarify if possible.
So, there are 5 flats converted in a big house.
3 phase supply, then into a meter for each flat, then out from each meter into an isolator for...
Sav
Thread
electricians' talk
inspection
inspections
installation
isolator
periodic
record
separate
supply
A neighbour of a friend had an extension built 3 years ago and although the lighting has been ok they have come to remortgage and don't have any kind of certs for the extension for the survey. The lighting was fitted by a guy not on a comp person scheme/part p registered and it clearly wasn't...
Simon_
Thread
advice
aus
circuits
client
extension
house
inspection
lighting
periodic
please
I have asked a letting agent customer of mine to consider having periodic inspection reports/electrical condition reports on the properties he manages, and he has agreed in principle, but the individual landlords of each property have to agree first before he can order the work on their behalf...
gmchris
Thread
aus
electrical
electricians' talk
inspection
inspections
landlord
landlords
periodic
property
their
Yippppeeeeeeeeee got my 3rd year NIC assessment at 1pm today with Eddie Bassett ! never had him before but all seem friendly enough ! oh crap i've run out of hobnobs ! let you all know how it goes !
Kung.
kung
Thread
annual
assessment
current
domestic
electricians' talk
equipment
periodic
thats
using
How can I work out the P-N figure of eight readings and the R1and R2 readings from the end to end readings of the ring cct.
This is because our certs are typed up as we go along on site, and I only do the end to end tests on the ring.
Can anyone help pls.
Hi, I've been asked to carry out a PIR on a Mobile Catering Van. As I haven't done one of these before, am I right in thinking that I complete as much of the forms as I can, just highlight the fact that the supply is from a generator and mobile? Schedules as normal using the generator for live...
jerrybouncer
Thread
attach
building
catering
electricians vans
electricians' talk
generator
mobile
periodic
section
van
vehicle
when doing a periodic inspect and test can anyone tell me at what point an unsatisfactory conclusion is required . i know that a code 1 is a definate unsatisfactory but what if u where to have 4 code 2s and 2 code 3s for example . is it down to disgression or is there a set amount of codes .i...
just done a PIR. found no bonding anywhere, including bathroom and to water and gas pipes.wasn't sure if i need to recommend RCD for the ceiling light in bathroom to cover that circuit or simply to put in bonding as it should have been done.the customer wouldn't pay for an RCD anyway so isn't...
Hi guys i have a few questions and would be great if someone could advise. Reason I'm asking is because of a difference of opinion between myself and another sparks, my answers are in grey (If I am wrong then my excuse is its been a year since I left college and all i have been doing since is...
darren
Thread
cert
electricians' talk
installation
other
periodic
question
questions
Hi all During r1 r2, ELI and PFC tests of a lighting circuit would it be a problem to leave lamps and ballasts etc in GN3 shows them out but I can't see a problem
Hello, recently asked to carry out PIR on property. There are test stickers on the cdu to so say it has been passed befoe however client does not have certification. Everything seems in order, but the water pipe thoughout the building is plastic pipe, so there is no bond. (No gas in use either)...
As per title, I have been offered some work doing periodic (landlord) inspections on quite a few properties. How much do you guys normally charge to do a 3 bedroom house?
What is the general opinion for time until next inspection for a holiday let property, I have always put 1 year, I know this can be somewhat a grey area but my understanding is that the duration between inspections should be dependent on how old the install is vs it's condition (ten years - new...
Just answered a question on another post ,and it dawned on me , yippee the brain kicked into gear , i have read on loads of posts that people say doing an inspection just calculate the R1R2 by doing a Zs and taking away the Ze , i have never liked this method and heres a reason why ...
nickblake
Thread
calculate
carrying
circuit
electricians' talk
light
lighting
lighting circuit
never
out
periodic
when
hi all,
i am currently an niceic domestic installer but i would like to be able to do periodics aswell which the domestic installer scheme doesnt allow. i spoke to the nic and they advised that i have to become an approved contractor to be able to do them. they said that i would have to show...
sinaloan
Thread
allow
aus
domestic
electricians' talk
inspection
periodic
reports
Hi All,
im C&G 2330 Level III qualified, with the 17th Edition but im not presently a scheme member, due to being really poor. I don't have my 2391 but aim to do so when l can afford test equipment.
My question: Am I permitted to perform a periodic, using calibrated 17th Edition approved test...
Hey guys,
I have been asked by a work mate it I can complete a Periodic Inspection Report for his brother who is in the middle of buying a house which the insurance company have required a survey of the electric's assessed.
I am booked to take my 2391 in July but they need the report sooner...
Spoon242
Thread
company
complete
electricians' talk
inspection
insurance
periodic