Why does it try to give you the value of 16KA in the drop down box for prospective fault current. Has anybody else come across this or do they know the reason why? I always put my measured value in but still would like to know the reason they try to give you the above value.
Hi all, most of my work is industrial, I'm required to test a consumer unit in a hydro generation unit.
This is not an issue I'm just struggling with the PSCC Live test as there is an industrial RCD directly after the incoming supply from Scottish power due to us having to supply our own earth...
Hey guys,
Hoping someone can point me in the right direction here.
So I have aquired the responsibility of looking after the PFC units on site, Problem being nobody knows anything about testing the caps including me!
So basicly they are 3 phase units with anywhere between 5 and 12 stages...
Hi all,
I recently went to install a new circuit & when trying to obtain a ze reading at the origin (TN-C-S) I got 0.01 ohms with a pfc of >19.9kA... This is when testing from the main distribution board which is in a hut next to the building where the work took place 15/20 meters away. Anyone...
Having a moment lol
please can someone clear this up for me.
my merger MFT 1730 displays the PFC as 955 A
Filling in a cert and it has the KA symbol by the box
should I be recording the 955 in Amps or should i convert it to 0.995 KA
Cheers
I have my Am2 this week and am getting confused with what reading is to be placed in schedule of test results.
I understand for PFC to take the highest reading between 3 phase and earth but have to then go between phases & N to find PSCC.
Is it PSCC reading then doubled and put on back of test...
Guys,
I'm aware that 3036's come in Type 1,2 & 3 with different max fault current capacities. What I don't know is how you tell the difference between the Types.
Also, if you assume a Type 1 at 1Ka, what would you code an installation with Type 1 rewireables with a PFC of 1.42Ka? The...
i have just done a test on a property and the pfc at origin of installation was 0.712ka. The 3871 mobs have a 6000a breaking capacity. I am a bit confused as I have read something about it always being higher anyway (16ka) for a fuse or main switch 100a or less. Any info here would be much...
Hi Folks, so doing some testing on an installation today and when i carried out the PFC test i was getting a reading of 11A? I tested and retested and kept getting the same result! So, the installation in question is a shed that has had a split load board installed (by someone else) which is...
Came across a PFC result on an EICR today of 10KA. My meter is calibrated and I carry out monthly checks with a check box to ensure the on-going accuracy of the equipment and all tested fine up to today.
Im not sure if I should quote my customer for C type R.C.B.Os with a higher breaking...
I did an EICR for a client over a year ago and as part i took the Ze reading at the incoming supply. All normal for a TNC-S it was about 0.14 ohms. I installed a socket in his workshop recently and as his tenant was in i could not remove the main earth so i took a Zs at the same position. The Zs...
Hi I'm currently coming to the end of my apprenticeship having completed my city of guilds level 3 and 17th.
i completed my am2 last week and passed everything apart from my testing and inspecting. I would just like abit of advice on how to complete the pfc test correctly as I failed on that and...
I seem not to have access to the professional forums so I post this here:
I understand ohm's law and to get a current you use Volts/Resistance (V/R); so if it's Perspective Fault Current (PFC), it's V/R or Volts/Ze; and we divided by 1000 to convert to kA. Yes?
Is there a difference when...
hi, fitted new consumer in a domestic house.
testing.
ze 0.16
zs at origin 0.04
pfc 6.2ka
the pfc is my problem, ohms law would make the pfc work out around 5.7Ka (using 0.04 as your resistance) (with all paths in place)
using megger 1553 two lead test, high current, pefc and pscc are the...
Hi fellas,
Doing a new build at moment, its had a new supply put in - Ze is 0.02 ohms, Pfc is 12kA. Besides changing all Mcbs for higher rated breaking capacity are there any other methods that could be used to make this install comply with regs? I asked a colleague who suggested applying a...
Hi,
If you have a TNS supply, you would have a separate earth path by way of lead pipe or split concentric etc... true?
Ok, so if you have a PME / TMC-S supply, the earth connects to the neutral at the service head, yes... true?
Ok, so just out of interest, if you had an overhead TT thats now...
Afternoon....
I have just completed an EICR and am unsure if the Wylex BS3036 fuses require a code due to their breaking capacity related to the PFC.
Firstly I would like to identify if they are S1A, S2A or S4A as that would solve the problem of the PFC being 1.35kA, however I dont think its...
Could anyone out there give me a detail explanation on what is the above test reading proving, is it that you have for a very low reading good continuity through the connections at the equipment at the origin of a installation. And what makes the reading vary from one installation to another.
Hey guys
im testing a TT System and the Rod resistance is 33 ohms. Which voltage / 33 is 6.969
which is greater than 6k rated on the mcb. What else can i do except increasing the rated mcb to 10k?
thanks in advance.
hi,
I did Ze test, I got 0.22 ohms but PFC test I got 22 Amps. it is very low. I am expecting a (230/0.22=1045 amp ) by theory
So pls let me why it is very low reading