Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported...
Typically the EICR I fitted in this afternoon because I'd hoped it would be fairly simple (new build home, 2007), turned out to be the only recent one that's thrown up a major FI.
Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB
R1+R2 fine, insulation test L&N -> E an immediate...
Hi,
I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests.
I know parallel paths could cause a low reading, but...
Hey people,
I did some testing for a sporadic RCD trip this week.
The customer did some playing about and narrowed it down to the garage.
Tested the garage circuits and all were good. Tested the feed and found with the CPC still in the bar I got 0.076 meg but when I pulled it out the fault...
Had a weird one tonight, with a new tenant who had a higher than expected first monthly bill.
Studio flat with one storage heater and off peak immersion, standard white Economy 7 meter with teleswitch.
Bulb had set the tenant up on their single rate tariff and happily accepted the two readings...
Hello,
looking for some advice on 2 things please.
Ive tested a ring main in a house with RCD protection, the results ive had are
L-L .43
N-N . 41
E-E 1.17
I had a look for a loose connection but can’t find anything, how high does the CPC reading need to be before you would consider it ‘to...
I’m doing some tests on my board at home in order to prepare it for an upgrade. It’s an old plastic GE board with no rcd protection. Doing continuity of ring final circuit on the main ring. When it comes to end to end tests at the consumer unit I’m getting no reading between neutrals. All good...
an eicr was carried out to an industrial plant area were the zs readings were all high readings above the maximum for a tns installation i noticed that the supply cable in question was getting monitored by an elcb. However recently the company or contractors. have driven in earth rods local to...
We are thinking of installing new ceiling lights, in Standard 10 feet ceiling. We originally have 4 inch diameter light in the hallway. My son would keep the door open to prevent getting hot, however this hallway light was hitting the side, peripheral of his eye, very small and lot of light...
hi
i have a 4kw samil power solar river inverter.
when i log on it reading for pv1 shows zero for pv 2
i checked both strings with multimeter and both show simmilar readings.
just to note its like this even when im getting over 3kw
Newbie Testing Question:
I am getting a very low IR reading between L&N on a kitchen ring (0.01M). The ring was working fine with no tripping before testing. Can anyone shed any light on what may be causing this low reading? Thanks
Ok so I have been to a domestic property today, and carried out an EICR, couple of issues flagged up with regards to the usual no RCD protection bonding cables etc now its quite a big property and the customer has gone with my advice of RCBOs but one question. Most circuits tested fine but the...
I live in the Philippines but I have the same US electrical system (2 x 110V hot + 1 x neutral). I have two ground rods buried 8 ft. deep and connected to the main panel. Netural and ground are bonded in the main panel. And from the main panel, all 4 wires (2L + 1N + 1G) go to sub panels. Ground...
Morning All,
Currently carrying out an EICR and going through ring final steps with the following readings:
r1: 0.31ohm
rn: 0.32ohm
r2: 0.03ohm
Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo)
When i...
Hello
I’m an Electrical improver based in Reading.
I have * EAL Electrical Installation lv2
17th Edition
Testing & Inspecting 2392
ECS
IPAF
Abrasive discs 2020 Ticket
Manual Handling 2020 Ticket
Working at height 2020 Ticket
All my experience has been commercial and industrial my last two...
Hi All,
Busy doing an EICR and on 2 of the Socket Rings for the dead test I get the following results:
Step 1: End to End (0.32 ohm r1, N ) & (r2 = 0.51 ohm)
Step 2: r1 to N 35.6 ohm
Step 3: r1 to r2 no reading
At first I thought maybe I was testing the wrong r2 in/out but I traced the cable...