ring final | Page 2

ring final

  1. V

    Ring Final Test - Neutral >19.99kOhms

    Just checking, what I think I already believe. Doing a pre-install test of some outdoor sockets on a ring final. So far, confirmed bonding, incoming polarity, Ze and Pfc and RCD Test on circuit, everything fine and within regs. However on testing Ring Final, Line came out fine (0.7), Neutral...
  2. J

    Coding for a Ring Final Circuit 1.5/1mm

    Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD is a 16a type B MCB. All testing has come back as expected for a Ring final that has been installed in 1.5/1mm and the measured Zs is well within max...
  3. mak

    Insulation resistance test on a ring final circuit

    Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other...
  4. E

    UK CPC missing on ring final

    Morning All, Currently carrying out an EICR and going through ring final steps with the following readings: r1: 0.31ohm rn: 0.32ohm r2: 0.03ohm Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo) When i...
  5. C

    Fault finding ring final RCBO

    Done a condition report on a old mains board, everything good apart from ring final, got 0.55 nn 33.7ll and 3.8 on ee, changed board to main switch and rcbos, carried out a full accessory swap on all sockets and fuse spares in house, found some bad practice, twisted lives, n and earth's, no...
  6. W

    7 core NYYJ cable to extend ring final circuit?

    Hi, Extending a ring final circuit off a socket in the kitchen through the wall into the shed on the other side. I already have 7 core NYYJ 2.5mm cable and I was wondering if I could use that to go through the wall to a J/B then connect to singles in conduit which would add about 4 meters in...
  7. J

    Diversity on a Ring Final

    Hi there, I'm just trying to get myself into cable calc and my first hurdle is demand and diversity. I understand the majority of what is coming across in tables A1 and A2 OSG but I'm just struggling to clearly understand what I should be using for demand on a domestic 32amp ring final...
  8. M

    Ring final no continuity on live ends r1

    Hi, Im new to fault finding, Im on a job where there is no live to live continuity on the ring final circuit which supplys the sockets to the whole house, with new flooring recently installed I cant access the floors, im assuming there are many jbs because its a 1960s property, if I connect one...
  9. samsingh

    UK Am2 - Ring final circuit

    Hi, I've sat my am2 practical today. I have a question about the ring final circuit hopefully there is someone who can relate. Is it crucial to wire the ring final a certain way? Ive bought 2 legs out, one goes into my closest socket which went down a bit of conduit and the other leg goes to...
  10. P

    UK Extending/breaking into ring final circuit

    I need to install some extra sockets in a kitchen. It's a single story ex-commercial kitchen. All the wiring is in singles in steel trunking in the loft space, with drops through steel conduit to the various sockets and switches. I want to install an additional 6 sockets under the worktop for...
  11. R

    Extending ring final circuits

    Hi. I have a CU move to do - around 5m from current location. There are 10 circuits, 4 of them ring finals. I'm considering whether to extend the rings 'as are', or to split the rings somewhere in their approximate middles and extend them to separate RCBOs as radials, the aim being to reduce...
  12. S

    Ring final circuit conductors and value Zs and R1+R2

    Hi all, I would like to ask you about ring final circuit canductors and schedule of test results. I have got dedicated ring circuit to supply kitchen appliances. Circuit is protected by mcb tybe B 32A. Then supply is split into radial circuits to supply appliances by switched 13A FCUs. What...
  13. P

    Radial or Ring Final Issues

    Hi all I have just moved in and am in the process of adding some sockets. Am I right in saying that I can add to the circuit regardless of which type of circuit it is as the MCB is a 20a, obviously as long as I'm using 2.5mm t+e not speaker wire etc. I get the issues with RFC where 32a fuse...
  14. Marcus Vaughan

    Shaver Socket from a Ring Final

    Hi All, A customer has asked for a shaver socket to be installed in his bathroom. The only issue is that there is no lighting circuit available (loft conversion above and no access to the eaves). His idea was to come off a socket in a bedroom on the other side of a stud wall to the proposed...
  15. Sparksaflyin

    clever ways of ring final test without removing spur fronts??

    Morning fellas. I know from regular visits to this website that we have some rather intuitive Sparkie’s on here so I thought I’d join in the fun. I’ve got a rather basic question to start with but also where some of you can hopefully show your tips and tricks. Im currently working on a...
  16. KeenPensioner

    Can't figure ring final r1 + r2 divided by 4

    Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring final and then joining incoming live to outgoing neutral etc, and I know that this configuration gives a figure of 8 (in fact can be straightened to...
  17. J

    Hand dryer off ring final

    HI everyone, Is it acceptable to wire a hand dryer from a ring final in to a 13 amp FCU. The ring main in question has 30MA RCD protection. Or, is it best to wire a new radial circuit for it?? There is a socket I can spur off that is easy to get to. Thanks
  18. Marcus Vaughan

    Power to an Outside Office - Spur from Ring Final?

    Hi All, Just looking for some reassurance on a job I've looked at today. My status is that I am trying to stay within the realms of 'Minor Works' until I get a bit of experience under my belt. Conscientious decision - but everywhere I go it seems that notifiable work is needed as well...
  19. Marcus Vaughan

    High(ish Zs and extending ring final question.

    Hi all. Love the forum by the way. I do have a question though... I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper. Thought I’d better do a live Zs test. Zs = 1.29...
  20. B

    Fault finding on ring final circuit

    Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top