Hi all. Love the forum by the way.
I do have a question though...
I have just visited a house (on a Sunday!). Customer is asking for additional sockets onto 32amp ring final. Circuit is 30mA RCD protected. Wiring is 2.5mm/1.5mm tinned copper.
Thought I’d better do a live Zs test.
Zs = 1.29...
Testing my extensions wiring today and noticed cpc fails continuity. Howevery I have continuity from outward leg to main earthing bar in CU
Any ideas how ?
So with megger leads they are not too happy in a kewtech socket tester so what do you do when you want to do this use kewtech leads on the megger? The megger leads clearly do not fit into the kewtech. Just use the plug lead?
Hi there
Been stuck on this for a while. What is the maximum r1+r2 reading possible on a lighting circuit in a domestic property. With a type b 6amp breaker.
Also if you guys could tell me about r1+r2 and rn Maximum readings for ring final.
Thanks
Hi All.
I had a job which was going to be a 'quicky' fault finding and repairing a couple of sockets, then it came to the testing.....
The consumer unit gave me no cause for alarm but was all labelled up wrong, so it turned out there were far more sockets and square meterage on this ring final...
Hi all. I know there is a DIY forum but im really after your expert knowledge rather than fellow DIY'ers/amateurs.
With regards to replacing a section of a bedroom ring final circuit in a bungalow loft what is your preferred method of cable routing taking into account insulation and not being...
I am planning to move a socket outlet. The CU is largely unlabelled so don't know which 32 MCB to switch off. There are 2 x 32a MCB. All other mcbs are for lights (6a) and a dedicated immersion (16a).
To isolate the circuit, I tried switching off the first of the two 32a mcb which isolated some...
After coming across countless faults in domestic premises regarding ring final circuits, I reckon they should scrap em...
Gets frustrating when you go to check
continuity and there is nothing between each leg. Or you get a call to check a burning smell from the C.U and once again a broken ring...
Testing a ring final circuit today. R1+R2 is fine, same as end to end r1 rn and r2.
However IR test is coming back 1.87M ohm. I split the circuit and located a section (one side of the ring is clear >999).
The customer doesn't want any walls or ceiling touched. As this is greater than 1M ohm...
Hi,
Went to look at a job today where the customer reported the RCD intermittently tripping.
I did an RCD Trip test and it failed to trip on x1, x5 or ramp test, the mechanical button tripped it.
After a bit of further testing I discovered that the Kitchen RFC had an IR reading of 0.00 meg...
Hope someone can help. When finding the cabling current capacity for a ring (wired in 2.5), would you use the data for 4mm in either/or table D5 of BYB or table 7.1 (11) in the OSG ? As the ring circuit is in effect 5mm !
Looking at the OSG ref methods; a 2.5 with ref method 101 says 17A...
Another straight forward job today has turned out to be a right mess once again so I thought I'd get some thoughts on the following before I start !
So an old MK LN59 board, feed to garage sockets on a single 2.5mm t&e from a 15A mcb and also spurred to feed a boiler on S plan,
Next ring final...
Hi Gents,
Have an existing circuit at a warehouse where a single 4mm 4core SWA has been used as a Ring Final Circuit. Two cores are in connectors in the back of the socket outlets thus creating a ring. The SWA is therefore the sole means of earthing. There are No banjo's at the sockets and the...
Hi guys. I need to check if I have a ring or 2 radial running from a fuse. I have an old wylex fuse box in which someone has put a blue 15amp fuse in a red 30amp carrier.
If I disconnect the 2 cables and check for continuity of the 2 lines then the 2 neutrals will this tell me if I have a ring...
Hello all
I used to believe that the power of circuit is running from live to neutral,then go back to the distributor.But when I see ring final circuit,I get confused...I know the power goes from both side of live cable,then it goes back to the circuit breaker?
Sorry about my poor...
My last thread was taken down due to copyright reasons, I think it was because I scanned a page from the wiring regs and posted it.
Can anyone tell me if this circuit design conforms to regs?
Started a level 1, completed practical assessment, was given test paper and tutor told me to answer these questions, bearing in mind I haven't had any theory practice or anything given to me on this information before hand.
1. Give TWO health and safety regulations related to assembling a 13amp...
testing a ring final today
end to end test L 0.24 N 0.24 CPC 0.37
figure of 8 L1 -CPC 2 L2 - CPC 1 0.25
L1 - N 2 L2 - N 1 no reading
IR >999
cant figure out why open circuit on figure of 8 any answers?
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc