split | Page 3

split

  1. S

    I know your not suppose to but in a split rcd DB can you change one of the rcd breakers for a normal breaker?

    I know your not suppose to but in a split rcd DB can you change one of the rcd breakers for a normal breaker?
  2. K

    UK RCD keep tripping.

    Hi All.. I have a 16mm 3 core swa feed a 9way split board in shed, 30m from incomer .. from the split board I have run a 10mm 3 core swa to 2 way board for hot tub. This has a 63amp rcd in it.. the other end at the split board is also a 63amp rcd on its own of one side of the split board.. this...
  3. S

    Are 30mA split load consumer units non compliant under 18th edition

    Hi All, Just wanted to see what peoples opinion is is installing a 30ma Split load board compliant/ non compliant under the 18th Edition or you have to use RCBO's for each final circuit? BS7671:2018, Page 155 regulation 531.3.5.2 is a note which says on TN systems which states " Exept where...
  4. robertl

    UK 480v Split Phase, new workshop, VFD's required

    Hi All, I've posted on here before about this, that time i was asking what people thought about phase converters as at that point i thought i could only get a single phase line at 100a for my new workshop. Turns out that after the DNO visited the site i can get a Split Phase connection put in...
  5. P

    LED Strip RGBW - How to split for parallel wiring?

    I'm looking to install some LED lighting strips to light some display shelving. It will consist of one driver going to a controller which will then be split into 8 x 1m length strips. I was wondering if anyone can give me an idea on how to split the power from the controller to each strip i.e...
  6. T

    'Particulars of the installation' for two submains split at the origin.

    At the origin, I have 25mm tails split to two fused switches. One 63a fuse protecting a 16mm (3 core SWA) submain to a DB (100a main switch RCBO board) at one side of the property and one 80a fuse protecting a 25mm (3 core SWA) submain to a DB (100a main switch RCBO board) at the other side of...
  7. B

    Radial circuit split 2 ways

    Hi all, working with a spark today, basically dodgy wiring in kitchen junction boxes everywhere, all ripped out, now all we’re doing is a new 6mm cooker feed and radial socket circuit, basically new 2.5mm radial circuit from CU to one side of kitchen where spark I’m with has decided to put a...
  8. B

    25mm split con sub main eicr code?

    Just done an EICR on a domestic, the sub main running from origin to cu is 25mm split con. Hard to know if its more than 50mm deep in walls etc without intrusive investigation. So could run with FI, but obv that doesn't deliver a satisfactory report. Bit of a tricky one as it would have complied...
  9. markthebuilder

    Split 3 phase across 2 domestic properties

    Hi gents I m looking for info comments advice that will help me look knowledgeable to my boss (money man) northen power grid. & mep consultant . I have been given a project to split 26 student clusters (6 bed) into 54 x 2 bed flats. current supply and metering to each student cluster is as per...
  10. M

    Split MCBs on consumer unit

    Hi all. How would you split MCBs where there are two ring final circuits (so better separate them). There is one electrical shower (will be on 40A). Any ideas? TNS system.
  11. J

    Circuit Breaker needed for Split Air-con with Inverter

    Hello all. I´m installing a new multi split Air Conditioning (Inverter Type) in my dwelling and I have to purchase all of the electrical parts needed for the installer. I am currently running a 63a Type-A RCCB and I was told by the electrician that I could use the Type-A with a 16a Type-C MCB...
  12. B

    PSCC on 460V Split Phase Supply

    Hi all. Been doing a bit of work on a pub out in the sticks with a 460V split phase Supply. When tried to test phase - phase PSCC my tester didn't play along. I was going to use the double p - n rule of thumb but then I got thinking, does this still apply to a 460v supply?
  13. C

    Split Concentric Termination

    I'm no expert on split concentric (assuming that's what this is)......But an earth clamp doesn't seem the best solution to this (also as the earth cores appear to be insulated! This is for an eicr on a sub main but I'll have to do the remedial work at some stage. Any advice on how to...
  14. Zdb

    Split load AFDD board

    Just seen that Screwfix are selling AFDDs for £200+:eek...
  15. R

    22 usable way split load NOT stacked

    Hi Guys. I'm in a tight spot and require a high integrity split load 22way (28modules total ) but NOT a stacked board but in a single row. I've seen one made by Proteus/M2 but Id rather not use CEF. Has anyone else come across one? Many Thanks in advance
  16. ipd1961

    Tripping issue with Split load Wylex DB

    Got an issue at home, today I got home and found one of the RCD's had tripped on my split load Wylex DB. I tried to reset but it wasn't having it. Switched all MCB's off on the RCD (Call it number 1) that had tripped then reset. All was ok, switched each MCB on and stayed in. Put the kettle on...
  17. N

    EICR - 2 boards, 1 with an off peak split and one with regular supply

    Hi there, im looking some general advice related to this eicr. im a bit lossed here, so would it be 2 eicr? or do i just splice two sheets together with the relevant information? on a seperate not i also noticed today when i had a wee look that his main water bond cannot be verified, is this a...
  18. M

    Low Ze, high(ish) R1+R2, Got a plan but just had an idea

    So Ze=0.02 and R1+R2 = 0.73 on a first floor ring main. Nearest submain is about 35m away, so that Ze's plausible, and even a slightly indirect route makes Ze=0.03 realistic. So MCBs are going to need changing to Type Cs. Unfortunately for that first floor ring R1+R2 of 0.73 is too high for a...
  19. B

    2.5kw split aircon unit on 20amp Radial

    I currently have 4 double sockets on a 20amp Radial, I am looking to get a small air con unit (2.5kw I think) to cool a 5m by 3m space. Bearing in mind the only things plugged into the sockets are 2 PC and 2 Monitors at most, do you think a 20amp feed is enough? It is a right pain to try and run...
  20. W

    Rcbos and mcbs split load board

    hello just checking a mix of rcbos and Mcbs on the same neutral bar is this okay ?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top