  1. C

    C/H supply - spurred or dedicated cct?

    OK then, long story short; relative has had her old (housing assoc prop) back boiler removed and a new combi installed. The plumbers left the combi's flex temporarily dogged into a plug top and plugged into a socket outlet over the worktop with the assurance that the sparks would be along the...
  2. A

    Volt drop on spurred lighting

    I have a run of garden lights to wire up, roughly 1000w so about 4.3A. If they are on an rcd spur from the ring main, is the volt drop allowed for a lighting circuit (3ish %) or for ring main (7% is it)? As 100m at 4.3A will require 4mm if my calcs are correct for a 3% Vd.
  3. spud1

    Spurred pump from lighting circuit

    Hi all. I have had a query from a client. We recently spurred a shower boost pump (400W) off of a local lighting circuit due to there being no local power circuit to connect to. We made an assessment of the lighting circuit loading, deemed it sufficiant to carry the additional load of the pump...
  4. C

    Single FCU Spurred from Spur?

    Another take on the 'spur from spur' questions. I'm in the middle of having an installation done and my contractor has taken a spur for a single FCU (for a cooker hood) from an existing spur (double socket). From the distant days when I used to do my own simple electrical work I thought spurs...
  5. J

    Easy Q. testing a spurred extension to a ring final circuit ?

    I have spurred out of the ring through a 3a FCU for an outside , how do i go about testing for a Minor Works Cert .Do i do the full RFC tests? or is there a quicker method ? The only tests are Earth continuity , IR , Zs and rcd i believe ....
  6. S

    Ring final fault - please help !

    I'm doing a PIR on my flat and I've come across a fault I can't work out. I'm getting a very low (about 0.1Meg Ohm) insulation resistance between Neutral and Line conductors on one of the ring circuits. However I'm not getting continuity between Line and Neutral and the MCB isn't tripping...
  7. G

    Cables burnt behind fused spur supplying immersion heater

    I went to a house last week where the live cable on the supply side of a spur (old colours, red) was coloured black as it had been burnt by what looked to be arcing due to loose connection. So i changed the old spur for a new one, as the old spur was all burnt and discoloured. Now the customer...
  8. D

    night mare job

    Trying to locate a ring circuit in a house and so far i have found 3 rings within rings..!! ARGH!!!!! CHIMPS!!!! :eek: any body else had similar encounters!!