testing | Page 4

testing

  1. M

    R1+R2 TEST. Tester clicking over and over

    Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over again. Any advice please? Thank you.
  2. cliffed

    EICR & IR Testing so many cables

    Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the Neutral/Earth connections are a nightmare to get at. The IR measurements are not good coming in around 0.154 MOhms. I'm hesitant in actually disconnecting...
  3. R

    Initial verification and testing

    Hi All I’m in charge of the maintenance (machinery and facilities) in a plastics manufacturing business. I have a ‘team’ of little old me and an apprentice! We have 7 (soon to be 12) injection moulding machines and 8 extrusion lines, so to say we are busy is an understatement. Anyway, enough of...
  4. sshdsilverado

    Testing sqD GFCI breaker

    Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or...
  5. punkin

    PAT testing a Ariston Andris under sink water heater

    Hi All I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix - https://www.screwfix.com/p/ariston-andris-lux-undersink-water-heater-2kw-10ltr/3248g Its a plugin & I’m trying to PAT test it. It doesn’t say which class its is under (1 or 2) I would assume...
  6. J

    Trace heating cable - testing issues

    Hi , Wondered if anyone can help , i currently install and test Trace Heating Cable on Mechanical Pipework for Frost protection . Recently our Clients are asking for a recordable test that states cable lengh of the circuit and a test to determine if there is a fault in the cable. Currently using...
  7. A

    Am2 3 phase testing procedure

    Hi got my am2 Tomorow and not sure on how to test continuity for 3 phase circuits, like where to link out also for IR test aswell
  8. L

    I.R. testing existing circuits

    The accepted method of I.R. testing existing circuits has been to join L and N together and test to E, to protect against damaging any electronics that were inadvertently left in circuit. However ,with the increase of new types of circuits between L and E as a result of "intentional leakage"...
  9. NackJich

    Parasitic drain need testing advice please

    Hello again. My car battery is draining completely overnight. I charged it up and ran it through a fairly decent battery tester which resulted in a GOOD BATTERY advice at the end. It tested charging, cranking response, load at 2500rpm etc. A known old battery was a fail, so I'm reasonably sure...
  10. Nexblue

    Brand New EV Charger - We need you for testing and more!

    Hi Everyone, After a long time of research and development, we are finally proud to launch our new smart EV Charger: The NexBlue Edge. Before we launch our new product officially, we would like to get professional electrician’s feedback on the installation and the usage, in order to be...
  11. _KaCe_

    Trouble shoot why a ground fault circuit breaker keeps tripping.

    I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit the outlets are on has a problem... the circuit keeps tripping. Question 1: I was wondering if there's a way to test the circuit breaker itself? Then...
  12. M

    Testing a garden vac

    The vac is a Flymo EV650. It needed a new switch. I found several but all of these were either rated 8 amps or not at all, & the plus has a 13 A fuse. So I looked up the manual online. It says: " 1 mm2 cable 10 amps" and "it must have a 13 amp fuse". But surely I must not use a 13 amp fuse...
  13. H

    Testing PFC on a three phase board with 100 amp From the meters tails

    I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a board I’m trying to do a pfc on the db but it comes up with 2 lead high which trips the RCD I tried on 2 lead low however came up with 20 amps which...
  14. D

    Changes to AM2 testing section causing more failures

    Has anyone else noticed that AM2 Testing now has 10 questions at the end and that they are a lot harder than pre-Sept22 AM2
  15. T

    Fault finding with a multimeter

    Hi, I’m just wondering what sort of readings I can expect for faults on a multimeter? I’ve only ever used a multifunction tester. What readings can I expect for a short cct fault or a polarity fault? I know that open cct will be 0L/1, cheers
  16. R

    Martindale HPAT400 opens with calibration screen

    Martindale HPAT400, previously working well, switches on with a calibration screen, not the testing screen, then turns off. Suggestions please?
  17. S

    DIY - Am I testing my EV charger RCBO correctly?

    Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if I reached the correct conclusion or whether I'm actually doing something wrong with the testing? I had an EV charger installed a couple months back...
  18. RMS Electrical

    Issues with erroneous testing

    Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V- 190V-240V on each of all 6 Live circuits of the RCD group. Whilst testing for erroneous circuits, I had isolated the mcb I was testing and energised...
  19. T

    LearnZone Media - Online Inspection / Testing course C&G 2391-52

    Hi, has anyone completed the CG 2391-52 inspection & testing course online with LearnZone Media recently? Just looking for opinions or feedback as it looks like a great way to refresh knowledge at my own pace before booking an exam...
  20. Chivers

    Electrician Jobs SW/Bristol area Testing & Inspecting role 30K PA

    Hi, I work for a company that is currently interested in recruiting an Electrician to be based from home and cover the M32/M4/M48/M49/M5 corridors and other motorway areas in the South of England. 17th/18th Edition with some Testing knowledge is desirable. PM if interested and 'll send you a...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top