Hi
Can anyone help ?
Recently fitted 2 separate Eaton 32a Type C RCBO, on the RCD test it fails to trip on the 1 times test and gives result as >400ms. It trips fine on 5 times test in 7.1ms. Using Megger 1552. They are fitted on 2 new 6m2 radial circuits with Blue commando sockets. IR results...
Hi all,
New to this forum. I have a weird scenario and wondered if anyone might be able to help.
I have a Grasslin timer socket switch (not digital) in my garage. This powers 4x lights outside my house. I have 70 Watt bulbs in each. When they are set to come on, at 6pm, it trips the...
Is there any particular reason why the trip times for RCDs at I and 5I are the values they are (300ms and 40ms).
Is there some particular medical reason why??
I'm just curious, no particular reason but may weave that into the conversation next time I'm in the pub!!
When visiting my parents, I noticed their PV invertor was showing zero W generated. On inspection, I found the MCB had tripped.
Is there any reason for an invertor to trip it? Powercut, or power surge?
The PV system is rated 3kW, and the MCB is 20A, type C.
We checked back the history on an app...
I have a Tefal 1000 deep fat fryer. It is the first time I have used it. Was given as new a few years ago.
I used the same outlet as I use for the kettle 2200w and a microwave 700w.
The Tefal was on for around 30 seconds and it tripped the RCD in the house electric.
Kettle works fine and also...
I am to replace an old MCCB with a new Eaton one, the circuit feeds a few boards and the current rating for the circuit is 160A. What I'm trying to understand is the 4 trip parameters that you select yourself on the breaker. These are:
IR - Continuous current setting (A)
tR - Number of...
Can I wire single phase into 220-240V 3phase trip switches/contactors etc.
What I am trying to do is protect a 220v-230v encoder but want the earth wires to look neat. professional looking.
Please see picture below
Hi Guys
Help! The 6 amp MCB for a downstairs lighting circuit keeps tripping, sometimes instantly, sometimes slowly. An IR check live to earth gives >200 Meg on the 250 Volt range (I don't want to blow up the dimmers!) when all light switches are OFF! This reduces to near short circuit when you...
Hi,
I'm new to the forum and to electrics in general, trying to study and get qualified and get practice where I can. One of my friends has asked me to help with his oven, which has been tripping the whole CU, but only after he's cooked in it and opens the door. Apparently someone looked at it...
Im specking a large 480a cable over 160m ive done cable calcs and come up with 2x 120mm 70c armored.
now Im trying to work out my max zs...with no avail.
my main ze is 0.17 but my mccb is saying max zs of 0.054 and my mccb will not trip... why is it so low?
its impossible to get my zs less than...
Hello, this morning I was having a shower with really really hot water. Shower lasts at least 15 minutes... at the end shower circuit breaker tripped.
It does not work any more, when I try to switch it on, it does not "keep the position".
I have a brand new circuit breaker, bought some time ago...
So hi everyone, i have alot of electrical items in my room upstairs. And if anything were to fail i would like a switch that would turn everything in the house off. If i were to have a red emergency stop button (normally open) and connect it to a plug so that the ground wire and neutral connect...
Hi Sparkys!
one to scratch your head with: randomly one switch light trip the rcd sockets on the board?
have a look at the pic if it helps..
thank you
Fab
We all know the side effects of a normal 6amp MCB operating more times than often when a bulb blows (especially gls or candle lamps) but has anyone ever tried to to eliminate or reduce the nusience tripping?
I have an elderly client with a 4way rewire able fusebox and I need to change for either...
Just in case anyone here has such things I am looking for a shunt trip and alarm (trip) contact for a Terasaki Tembreak XS400 NJ mccb.
Please PM me if you would like to sell me such items.
Just put a Split Board in my own house (a bit of a upgrade going on) and a problem with one of the RCD's.
Last minute post this and stopped work for the night.
I have not done any fault testing at the min, as having a relaxing Friday drink. However Fully weird every thing but with the...
Hi guys, first off im not a qualified electrican but i am a qualified engineer and very competent, also assisted a few rewires to help a friend start a buiseness a few years ago.
So to the point. I recently bought a new house and its had a full rewire as all the cables are new colors and it...
Hello
I'm a Level 2 electrical installations student and I have a question about Type B BS60898 circuit breakers.
I've been revising tonight and have noticed that the trip time on these is 3 to 5 times the rated current. What does this mean?
Say I had a 32A Type B would it trip over any...
I was called to an office in a field today (tt system)
The led lights and sockets (separate circuits ) still have power when switched off at the switches ( lights on dim and socket neon half bright)
I did a ze test at the board and had to replace the earth rod.
The reading at the board is...