Going to a garage tommorrow were they have just had new LED lights installed.
After a while the photocell overload breaker trips, the photocell is connected to a contacter the RCD protecting the whole circuit never trips.
The light units that have been installed are approx 1/3 of the wattage...
I have just installed a new wylex dual rcd board replacing an old memera 2000 single rcd. Whilst wiring in I noticed what was purporting to be a ring main was in fact two radials in the same breaker, no problem I thought, I will split them up, one on each rcd, however, having done that it will...
Hi all,
On a ground floor ring main protected by a 30amp bs3036 rewirable fuse the owner has reported the 100ma rcd trips out on any occasion where her bathroom extractor fan is on at the fused spur and she tries to use the Hoover.
After looking at her bathroom extractor fan, I've seen that...
Been called to a fault today customer saying RCD tripping when under load.
I go rcd holds in till he plugs something in that say uses more that 50w, I try and ramp test rcd - no trip, 5x no trip, 1x no trip, rcd test bottom - no trip. so I think it’s a faulty rcd, i put a new rcd in and test...
Tris Zanker
Thread
earth
electricians' talk
fault
meter
neutral
something
trips
Hi all. Got a bit of a problem. When we get heavy rain like we did today, the RCD trips. So i push it back on and sometimes it will stay there for months or it sometimes again instantly. Any idea what the problem is? I do have 2 outside lights and a PIR sensor on them. Im thinking the problem...
AshFR
Thread
circuit
electricians' talk
get
heavy
lights
outside
problem
rcd
trips
when
As above, came to commission a circuit yesterday and got to the last step (test the RCBO) and on 3 attempts the main RCD went instead. TT installation, no markings on front of RCD but assume must be 30mA non time delay.
The obvious answer is quote them to swap for a type S RCD but it's a big 3...
Hi guys, need some advice please. I've got a problem on a French 3 phase CU. Basically the 3rd phase rcd trips when the boiler circuit on the 2nd phase is on whilst a sockets and lights circuit on the 3rd phase is on. If i turn off the sockets and lights mcb (there on the same circuit) then...
Fitted a socket for a customer today, Job done.... 2 hours later call from the customer " All my power is off" turns out to be the rcd tripping, Went back checked the socket and all was fine, checked the rcd with the socket unscrewed from the wall and no problems, screwed the socket back and rcd...
HI Guys
I've had a call back to a job. It seems that a 6A light circuit mbc trips when some kitchen downlights are turned off and occasionally on. Its an intermittent fault. I replaced a light switch on this part of a circuit and looked a a poor contact on a 12v fitting (its a return to fit...
Fitted a standalone fused 30mA RCD unit today protecting a spur from existing circuit wired directly from MCB in CU. RCD FCU is mounted adjacent to CU. CU has 100mA RCD upfront (Crabtree) & is populated by 60898 MCBs. 30mA RCD x1 test was fine (28ms) but the x5 test trips 100mA as well as 30mA...
Hi all
Job on a farm, which is TT, The supply conductors go into a 100 amp 4 pole RCD Mainswitch ( In a plastic Enclosure) Then off to an MCCb Board which then feeds Several sub mains around the farm that all Have 30 Milliamp RCD Mainswitch
Problem the customer has is when their is a fault at...
Welshsparky
Thread
electricians' talk
fault
help
installation
mains
supply
trips
just been to a job , saw that the shower 9.5 kw is on 6mm t&e the cable goes in the wall and under floor boards ,No insulation, to the board (A cable run of no more than 10 m) . I said downgrade the shower to 8.5 max. Is it really necessary ? never quite sure , its borderline to me .
Two jobs both identical with panels and invertors ect. Ie: Aurora 3.6 TL , 14 panels 235w. Both using Wylex garage boards 16amp mcb and 63a 30ma RCD 4mm T&E. One starts up and works no problem the one next door trips RCD. Done all checks and test all ok. Invertor goes through start up all ok...
Hi there,
I've got an old, Wylex, 4-way, rewireable fusebox, water mains providing my earth (PME to come) and a 100A service fuse. The circuits are:
i) ring main
ii) lighting (two circuits in single fuseway, one of which is a single light)
iii) immersion heater (not used)
iv) cooker and hob...
Any one else come across the new 2 lead no trip feature trips some brands of rcbo's? so far i've found it trips wylex, crabtree and doorman smith. is their any work around or have i just got a dodgy meter?
Hi can any one help?
I have a customer that says his lights keep tripping out when the shower is on in the ensute and bathroom at seprate times, the wiring is 4 years old the lights are mains gu10 (not ip rated) there is a inline fan with a lv light in it, there is no sign of moisture and no...
:cry_smile: My facial expression with this job I can't figure out.
Hello first post on here and been searching to see if they was a post like this online.
In a church building, there is a 3 phase board that feeds a wylex single phase ccu with a swa cable 3 core but not sure on size, my best bet...
Brace56
Thread
3 phase
aus
board
electricians' talk
out
phase
single
single phase
trips
Hi guys, I've got a customer who's rcd is tripping every few days.
Any tips on the process to follow cause it never trips while I'm there.
Ive tested the unit itself and it's working ok?
Thanks