Just recently finished 2330 level 3 at college and also passed 17th Ed. I've been asked to do a bit of work for a friend of the family - outside light and add sockets to kitchen. Am I correct that if the main protective conductor and bonding are not up to the latest regs then they have to be...
Hi all
Am I correct by saying if I install a new consumer unit, like for like replacement with no additions I don't have to upgrade main protective bonding conductors if they are 6mm, aslong as there's no signs of thermal damage. Tnc-s system.
Would I note this on departures on electrical...
Hi, just a quick question I am upgrading a cu and partial rewire. Now the tails from the cutout are 16mm and go in to a teleswitch, they then comeout and go in to a multiwatt reader then in to the ccu. Obviously I want to use 25mm tails after the meter so do I get the electric board out to...
Continuity test results from the board to the isolation valve to the house and from the board to the nearest radiator has o.oo resistance on a 4mm cable do i still have to upgrade to a 10mm.
It means ripping up the floor and kitchen units in the kitchen and laminate in the hallway to put in a...
Hi guys,
i need to carry some work out to get my house to pass its mortgage retention, i had a mate from napit come round and do a electrical installation inspection condition report, as one of the retention on my mortgage is due to the old electrical installation. at the moment there is a 15...
Good afternoon folks,
I'm a first time poster - I've come here with a multitude of questions so you'll have to forgive me! I'm a fairly young engineer with limited design experience and I have been presented with a problem that I'm not sure how to solve. It annoys/embarasses me that I can't...
Hello all.
I am upgrading my bungalow fuse box to a new split load CU. My circuits on the fuse box were, 1. Cooker, 2. Heat pump and sockets, 3. Immersion heater, 4. Lights.
My new CU is a split load CU, to which I decided to separate the circuits between 2 RDC's in the following way, (From...
Hi All
My first post so please bare with me. I am a landlord and currently refurbishing a property. I called in a local electrician to get a quote on having a kitchen extractor fitted, and he basically noted the following things:
- ALL wiring (sockets, switches, lights) in the property is...
If asked to replace a BS3036 fuseboard with a Dual RCD Consumer Unit, you would have to test all circuits being connected to it etc for the EICert.
But, while doing this yesterday I have to admit that I realised that I don't know what test result would indicate that an RCD would trip if 'put...
I will registering with elecsa soon and going to change c.u in my flat for assessment. Line conductor is 10mm,Earthing conductor is 10mm and bonding conductor is 6mm . I don't know cut out fuse size as it is sealed. The c.u. only has 6 circuits. O.S.G says these are minimum required. Do I need...
Hi Guys, have any of you owners of the above tester encountered issues when flashing the device?
If I hold the up-arrow and light keys down and switch it on it becomes unresponsive and requires a battery removal to switch off.
If I hold the up-arrow and light keys down and plug in the charger...
Hi everyone
I'm installing a Samsung induction hob - all 4 hobs total 7.6kW
Am I to apply diversity to this to work out the fuse size? I can imagine the 4 hobs being used at full throttle quite regular and don't want to put it on a 32A fuse and it keep tripping if I put it on a 32A fuse -...
Just done a domestic CU change. The cutout was 100 Amps (used to supply Economy 7 storage heaters but no longer). Existing tails 16sqmm. Therefore need to change to 25sqmm as normal.
But existing tails are routed out of the top of an external flush meter box up through the (uninsulated) wall...
hi guys
hoping you could give me your thoughts,
i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.
its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the...
Hi Guys
Just been asked to upgrade shower cable from 6mm to 10mm and as not done other than when doing full rewires do i issue a minor works or a full cert
thanks
new fuse board with 5 circuits plus bonding, wiring a radial and lighting in the garage all surface, changing 4 light fittings, turning 10 single sockets into doubles, adding 3 extra sockets on the ring. wondering whats a fair price for this work?
Hi, i need to add a sub main to an existing supply for a second cu from which i will wire the extension, an out building and a barn. The existing supply is 100a and protected by a 100a 1361 fuse at the incoming service head.
This supplies the main cu which has the following circuits:
Shower...
Hi all you guys/gals out there was wondering if anyone could offer advice on the following:
I was recently asked to fill in an upgrade of supply form for a customer. A fabrication company. I went out to the premises and took some readings of their consumption. They have a 100 amp 3 phase...
Newbie here - please go easy on me, and I hope I'm posting in the right forum! ;)
Existing arrangement as follows - single phase TNC-S supply provided in a remote building. This building has a substantial 3-phase company supply, but my supply is tapped off the incommer, and through a a single...
Should one insist to the customer to have a PIR before proceeding with a CU upgrade? if not what do you do if there are hidden nastys ie bad IR readings?
Thanks
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc