Like that?I hadn't seen Avo Mk8's post when I wrote my last post. We've both written the same thing.
Yes, feed the L2s with the 'live' already present near them, then 6 wires between the two sites. These can be 2 x 3&E or 3 x T&E.
What none of them can be is a repurposed earth wire.
100% the same circuit in the CU. Cant I just use for example 3 core YY cable instead of 3+E? Both boxes are already grounded by feeding cablesThat appears correct. All earth wires must be connected at at least one end to the incoming earth wire, which should be tested to confirm it does actually connect to the supply earth terminal. It is preferable that they're connected at both ends.
It should also be confirmed that both incoming lives are actually part of the same circuit.
No for reasons stated in #16 as one of them will be insulated green and yellow and the cable itself should contain a cpc or earth conductor.Cant I just use for example 3 core YY cable instead
My point is... do I even need to run earth conductors between boxes or 6 wires between L1's and com's would be enough? Will I be actually achieving anything doing that if both boxes are already grounded?No for reasons stated in #16 as one of them will be insulated green and yellow and the cable itself should contain a cpc or earth conductor.
Yes, the cables between the switches should include an earth conductor that is terminated at at least one end but preferably both ends, ie both switch boxes per post#18My point is... do I even need to run earth conductors between boxes or 6 wires between L1's and com's would be enough? Will I be actually achieving anything doing that if both boxes are already grounded?
Just to confirm your latest diagram does match what's been discussed, and should work!Like that?
View attachment 121524
Do I need to connect earth wires in the strappers to terminals in the back boxes or can I leave them loose?
Will do. And I appreciate there are regs and they have to be followed, which Im giing to do. Only trying to find a justification, I guess I just like to know a reason I do something. I wonder if anyone actually knows what is achieved in this case by running earth conductors to already grounded boxes and why it needs to be done (except regs of courseJust to confirm your latest diagram does match what's been discussed, and should work!
Don't ignore the guidance given here about earth conductors - Include them to comply with the regs, e.g. use T&E to do the cables between the two locations.