0.00ohms,looptest at board. | on ElectriciansForums

Discuss 0.00ohms,looptest at board. in the Australia area at ElectriciansForums.net

M

mazo

hi,folks
can anyone tell me why i get a loop value of 0.00 ohms at the supply to a sub dist board (incommer)but when i loop test at the sockets off the board i get what's expected 0.34 and so on.
appreciate your knowlege guy's
thanks
mazo.:)
 
hi,folks
can anyone tell me why i get a loop value of 0.00 ohms at the supply to a sub dist board (incommer)but when i loop test at the sockets off the board i get what's expected 0.34 and so on.
appreciate your knowlege guy's
thanks
mazo.:)
Maybe a very good earth?Maybe very close to supply transformer?
Any other ideas?
 
thanks mrloy99
the board is connected to a rising busbar,fed in about,150mm swa,but i thought i should still get the value of ZE +R1ANDR2 of the supply cable.of at least 0.01
mazo
 
Had something similar once, it turned out the meter was faulty. I never found out why sometimes it seemed OK and other times read 0.00?? Didn't like the low readings.
The meter got worse and then read 0.00 for every test, cost ÂŁ70 to fix + calibration extra, they never told me what they fixed, I guess they just changed a circuit board. Like most equipment nowadays, there are no user serviceable parts.
Hope this helps.
 
I've seen a Zs reading of 0.00 ohms at the incomer of a sub board before. The bonding to the steel framework of the building which had footings buried deep in the ground was the reason. Not a problem, just it leads to high Prospective Fault Currents. Such is life!
 

Reply to 0.00ohms,looptest at board. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top