0.4 seconds or 5 seconds | on ElectriciansForums

Discuss 0.4 seconds or 5 seconds in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 9, 2020
Messages
46
Reaction score
6
Location
UK
Just a quick question. This might sound like a stupid question so apologises. I'm slightly confused with the regs 18th edition when it comes to disconnection times. So I was taught in college that in the 17th edition that when a circuit is less than 32A then the maximum permitted time is 0.4 seconds and anything over 32A then its 5 seconds. Now in the 18th edition has it has been changed? So that anything under 63A supplying socket outlets its 0.4 seconds and anything over 63A its 5 Seconds. And also why would you have socket outlets on a 63A breaker when it should be on a 32A ring or 20A radial. Sorry if those questions sound stupid, it's just I can't get my head around it for some reason. Thanks.
 
Just a quick question. This might sound like a stupid question so apologises. I'm slightly confused with the regs 18th edition when it comes to disconnection times. So I was taught in college that in the 17th edition that when a circuit is less than 32A then the maximum permitted time is 0.4 seconds and anything over 32A then its 5 seconds. Now in the 18th edition has it has been changed? So that anything under 63A supplying socket outlets its 0.4 seconds and anything over 63A its 5 Seconds. And also why would you have socket outlets on a 63A breaker when it should be on a 32A ring or 20A radial. Sorry if those questions sound stupid, it's just I can't get my head around it for some reason. Thanks.
You can get 63 amp industrial sockets
[automerge]1598043950[/automerge]
Just to add the disconnect time are the same as the 17th for fixed equipment and distribution circuits it's just for socket outlets that have changed .
 
You can get 63 amp industrial sockets
[automerge]1598043950[/automerge]
Just to add the disconnect time are the same as the 17th for fixed equipment and distribution circuits it's just for socket outlets that have changed .

Oh yeah I cabt believe I forgot about those. They are 3 phase sockets. Thanks
[automerge]1598044279[/automerge]
You can get 63 amp industrial sockets
[automerge]1598043950[/automerge]
Just to add the disconnect time are the same as the 17th for fixed equipment and distribution circuits it's just for socket outlets that have changed .
So just to clarify, previously in the 17th edition did it only Include sockets upto 32A but now in the 18th edition it includes sockets upto 63A?
 
Oh yeah I cabt believe I forgot about those. They are 3 phase sockets. Thanks
Yes you can also get single phase ones aswell
[automerge]1598044361[/automerge]
Oh yeah I cabt believe I forgot about those. They are 3 phase sockets. Thanks
[automerge]1598044279[/automerge]

So just to clarify, previously in the 17th edition did it only Include sockets upto 32A but now in the 18th edition it includes sockets upto 63A?
Correct
 
It's also different for TT systems, just to complicate matters.

For a TN system it's 0.4 seconds for final circuits up to 32A (without socket outlets) or up to 63A where there are socket outlets (this includes the industrial sockets mentioned by Flanders that can be rated at 63A).

In most domestic situations you won't generally see a socket circuit above 32A as you say.

On a TN system, for any other distribution circuit or circuit not covered by the first rules 5 seconds is permitted.

For a TT system, the times are 0.2 seconds and 1 second respectively.

This is all assuming 230V AC - they are different again for higher voltages.
 
It's also different for TT systems, just to complicate matters.

For a TN system it's 0.4 seconds for final circuits up to 32A (without socket outlets) or up to 63A where there are socket outlets (this includes the industrial sockets mentioned by Flanders that can be rated at 63A).

In most domestic situations you won't generally see a socket circuit above 32A as you say.

On a TN system, for any other distribution circuit or circuit not covered by the first rules 5 seconds is permitted.

For a TT system, the times are 0.2 seconds and 1 second respectively.

This is all assuming 230V AC - they are different again for higher voltages.
Right I'm starting to understand more now. Thanks for the help.
 
Right I'm starting to understand more now. Thanks for the help.
Some of is slightly moot other than correctly filling in certification, since RCD protection is now almost across the board in new installs so disconnection times are easily met.

It does make sense that anything with a socket outlet should be 'safer' since at some point a human will be plugging or unplugging things.

Maybe the change had something to do with car charging points becoming more common, (though I think they're 32A mostly at the moment) or to cover any possible use of higher power sockets to come, but that's purely guesswork..
 
The most common case (TN) for the 5s disconnection is on a sub-main, there are two reasons for having a longer ADS time:
  • Potentially better selectivity with downstream OCPD (generally with a fused sub-main feeding a sub-board with MCB) where you would design for as high a fuse rating as safe (ADS time & adiabatic limits)
  • On high current circuits the supply Ze might not allow a faster time in any practical choice of cable, etc.
Generally when most down-stream circuits have 0.4s anyway on their OCPD.

In the TT case you have two other factors:
  • A fault will likely raise the whole earth system to close to live voltage (as Ze/Ra is much higher than the supply R1) - so you really don't want that to persist too long
  • Due to this high Zs, you have no real options other than RCD to meet disconnection on an earth fault
Once you see that RCD are pretty much your only choice in the TT case then the times make more sense:
  • 0.2s is enough for instant/personal protection RCD
  • 1s allows for a delay RCD to have selectivity with downstream RCD/RCBO
 
Last edited:
It's also different for TT systems, just to complicate matters.

For a TN system it's 0.4 seconds for final circuits up to 32A (without socket outlets) or up to 63A where there are socket outlets (this includes the industrial sockets mentioned by Flanders that can be rated at 63A).

In most domestic situations you won't generally see a socket circuit above 32A as you say.

On a TN system, for any other distribution circuit or circuit not covered by the first rules 5 seconds is permitted.
Just to add if the TT system has all the bonding in place and protected by an over current device then you use the disconnection times for a TN system
For a TT system, the times are 0.2 seconds and 1 second respectively.

This is all assuming 230V AC - they are different again for higher voltages.
The most common case (TN) for the 5s disconnection is on a sub-main, there are two reasons for having a longer ADS time:
  • Potentially better selectivity with downstream OCPD (generally with a fused sub-main feeding a sub-board with MCB) where you would design for as high a fuse rating as safe (ADS time & adiabatic limits)
  • On high current circuits the supply Ze might not allow a faster time in any practical choice of cable, etc.
Generally when most down-stream circuits have 0.4s anyway on their OCPD.

In the TT case you have two other factors:
  • A fault will likely raise the whole earth system to close to live voltage (as Ze/Ra is much higher than the supply R1) - so you really don't want that to persist too long
  • Due to this high Zs, you have no real options other than RCD to meet disconnection on an earth fault
Once you see that RCD are pretty much your only choice in the TT case then the times make more sense:
  • 0.2s is enough for instant/personal protection RCD
  • 1s allows for a delay RCD to have selectivity with downstream RCD/RCBO
Just to add for TT system if all the bonding is in place and there is over current protection for the circuit (so most installations) then the TN disconnection values are used.
 
I asked a similar question recently and think it was Ian1981 who answered but there is another question I wanted to ask.

If you look at Table 41.1

[ElectriciansForums.net] 0.4 seconds or 5 seconds

and Cmin - UK voltage can go up by 10% so 240v and 250v TN systems have a disconnection time of 0.2 seconds ? is that correct ?

0.07s TT? not a figure I've ever heard.
 
Last edited:
If you look at Table 41.1

and Cmin - UK voltage can go up by 10% so 240v and 250v TN systems have a disconnection time of 0.2 seconds ? is that correct ?
That table is for the nominal voltages to Earth. So the typical UK domestic and most industrial LV supply is defined as 230V Uo (but +10% -6% range) hence it falls in to the 2nd column for Uo <= 230V

The 0.07 TT time would be for something unusual like a 400V phase-to-neutral / 690V phase-phase supply for big industrial stuff.
 
That table is for the nominal voltages to Earth. So the typical UK domestic and most industrial LV supply is defined as 230V Uo (but +10% -6% range) hence it falls in to the 2nd column for Uo <= 230V

The 0.07 TT time would be for something unusual like a 400V phase-to-neutral / 690V phase-phase supply for big industrial stuff.
makes sense, seems so obvious now?‍♂️, Thanks:thumbsup:
 
Just to add for TT system if all the bonding is in place and there is over current protection for the circuit (so most installations) then the TN disconnection values are used.

I've always read that as where disconnection is achieved by an overcurrent device rather than by an RCD, meaning that it only applies where the Zs is low enough to blow the fuse or trip the breaker, which is very rare in TT installs

Have I been reading that wrong? In most TT installs the RCD will trip first for a L-E fault and in that case disconnection is not being achieved by an overcurrent protective device.
 
I've always read that as where disconnection is achieved by an overcurrent device rather than by an RCD, meaning that it only applies where the Zs is low enough to blow the fuse or trip the breaker, which is very rare in TT installs
That is the note on Table 41.1 where it states if it disconnect on OCPD and has all the supplementary bonding then the TN times apply.

If it walks like TN and quacks like TN...

That would be pretty rare! Though I guess it might apply to a low current circuit with a fuse or MCB in the 1A or so range and above-average earth rod conductivity, or maybe a steel frame building that has an exceptionally low Ra in the 1 ohm or less region depending on MCB choices, etc.
 

Reply to 0.4 seconds or 5 seconds in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
362
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
328
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
302
I well remember the sliding windows on ther Mini, and also the manual choke and the foot-operated dip switch. I recently traded in my 18 year old...
    • Like
    • Informative
2
Replies
18
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top