Hi,

As per title, how would you feel about connecting a few garage lights onto some 0.75mm flex straight into the 6A MCB, ignore switching, just that its 0.75mm.

I have to say I normally go via a FCU but in this occasion I don't feel I need to as its in the garage with a 6A MCB I can come off.

referring to table 4F3A on page 378 it states 0.75 can take 6A.

id say I'm good to go, I k ow I'm probably stating the obvious but it's not something I usually do, hooking such a small co doctor up to an MCB.

reason for it being small is due to the fact I'm using 3 core and earth flex so I can use the switched output on the lights so they Interconnect on PIR.
 
Any takers about my post #8 and the regs stating a minimum csa of 0.75mm for the use of flex ?

I think it's open to interpretation.
I read it as the minimum size for a lighting circuit is 1.0mm and a power circuit is 1.5mm then flexes which are not part of a such general circuits (ie appliance tails etc) are restricted to 0.75mm minimum
 
I didn't know one existed, it's s shame you can't get 3A breakers across the different brands, o don't know if I'd have much need for one to be honest, but then there's always that once!

You get all different sized breakers across most decent brands. The lower sized (<6A) breakers are generally produced for panel and control applications as I understand it, they just won't be classed as 60898, or rather just 60898.
 
You get all different sized breakers across most decent brands. The lower sized (<6A) breakers are generally produced for panel and control applications as I understand it, they just won't be classed as 60898, or rather just 60898.

I did wander if that was the case Andy. But just had a look at the MK tech spec. See the approvals bit just below the table:



[ElectriciansForums.net] 0.75mm Flex into 6A MCB
 
I think it's open to interpretation.
I read it as the minimum size for a lighting circuit is 1.0mm and a power circuit is 1.5mm then flexes which are not part of a such general circuits (ie appliance tails etc) are restricted to 0.75mm minimum

For table 52.3 I would interpret this as meaning that if there is a connection to a mobile piece of equipment such that the connection needs to be flexible then 0.75mm² sheathed or non sheathed cable may be used.

Yep I must concur with you guys that the description in table 52.3 "for any other application" listed for flex actually should mean "for any other application than those listed above"
I have always worked to the 1mm for lighting and 1.5mm for power rule myself, just this thread prompted me to look up the table and question it. I also have never considered flex a suitable selection for fixed wiring other than for fused down circuit extensions.
Still an ambiguous table though in it's wording.
 
Hager actually do a large range in Type C which I suppose is quite acceptable to use on a normal circuit.

MCB 10kA & 15kA Type C MCBs

They should be available from most DB manufacturers, they won't be available for ranges exclusively intended for CUs though.

Can you use them for general/standard circuits? I see no reason why not, but undoubtedly someone will be able to come up with a reason why not.

7.5A was a reasonably common size once upon a time. I've seen a lot of 3871 MCBs in this size.
 

Reply to 0.75mm Flex into 6A MCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top