I know it depends on its inststallation method but what is the max current carrying capacity of 1.5mm swa 3 core?
If im looking at the correct table 4D4A it says 18a clipped direct.
But then this manufactures spec says 32a. (page 3) http://www.alertelectrical.com/upload/pdf/329armoured.pdf
I want to know if its acceptable to run a radial to 2 x outdoor sockets using 1.5mm SWA on a 16a mcb
looks like youve answered your own question then sidI'm with you on this one pevvers..
No one has yet given a valid reason and explained why they wouldnt use 1.5mm SWA on a 16a MCB, or even 20A MCB for that reason.
Ummmm, am I protecting the cable from overcurrents?
Yes.
Whether it be lighting, sockets, FCU's, it matters not as long as the cable and all associated equipment is protected from overcurrents, will disconnect in the required time, etc., etc.
Just because it's 1.5 doesn't mean it can only be used for lighting, just like you could put in 16mm radial circuits for sockets if you really liked, although you would have a hell of a time getting them in the terminals!!
As long as the calculations add up then you are complying with BS7671, which is what I adhere to.
lolI'm saying nuffin...
![]()
Couldnt be bothered to trawl through all the posts so sorry if I'm going over whats already been said.
Do the calcs & if all complies then just use the 1.5mm, nothing wrong with 1.5mm used for sso's if it complies.
Just because the norm is 2.5 don't mean you have to use it after all what size conductors would you use for sso radial circuit if MI was the cable of the day & you are thinking of proffits in the job.
Dont be drawn into this is the norm & this is how we have to do it, thats why your taught how to calculate cable selections![]()
now MI is a totally different ball game, op was for opinions and thats what he gotCouldnt be bothered to trawl through all the posts so sorry if I'm going over whats already been said.
Do the calcs & if all complies then just use the 1.5mm, nothing wrong with 1.5mm used for sso's if it complies.
Just because the norm is 2.5 don't mean you have to use it after all what size conductors would you use for sso radial circuit if MI was the cable of the day & you are thinking of proffits in the job.
Dont be drawn into this is the norm & this is how we have to do it, thats why your taught how to calculate cable selections![]()