It's not a shared n. Been working for the past year they said. IR test 0mohms between L and N.

Could damp cause it to trip after 10 secs? Why dies it happen after that long. Surly with a short it would trip straight away?
A low IR test with a megger tester doesn't indicate a 'short' it indicates an insulation or earth leakage fault. Just incidentally if it's an RCD tripping fault why are you testing between the L+N instead of linking the L+N together and testing to earth?
 
If we can get down to the nitty gritty of what tests you have conducted and how....it may shed some light (good pun) on whats causing the fault
 
Jiga, for hell's sake there's a procedure for fault finding. It's fairly basic stuff.
Put together a list of what tests you have carried out and how you have broken the circuit down and then maybe we can help you out.
 
I love it when Trev starts to get mad. All northerners have this perfect zone where sarcasm and honesty are perfectly merged.

I do think the OP gave up though
 

Reply to 10 second trip in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top