I have known on instances where a DNO will install a 100mA RCD (which then becomes the property of the consumer), where installations are very close to sub stations and have very high PFC and PSSC.

And why would adding an RCD to a circuit with a high PFC be of any benefit?
 
I have known on instances where a DNO will install a 100mA RCD (which then becomes the property of the consumer), where installations are very close to sub stations and have very high PFC and PSSC.

Which DNO? I've read a lot of ukpns new service design paperwork and never yet come across this.
Also I can't see what the advantage could be for a high pscc? An RCD would not do anything except perhaps melt under excessively high short circuit current
 
Haveing re-read Spins post and actually paid attention this time , I thought he had mentioned that it was because of a high Ze which was the reason why it had been done for the ones I have seen .
 
Nope, nothing to do with high Ze, in fact one would expect very low Ze in such situations.
As to the why of it, I have no idea, I do not work for a DNO.
It sticks in my mind because the DNO installed the RCDs, then washed their hands of the devices, handing over ownership to the consumer.
Only mentioned it, as a possible explanation as to why the device is present.
 

Reply to 100mA RCD Incomming NOT TT but PME in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
987
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
812

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top